Thank you guys for your input!! 

I just had another AHJ bring up section 8.4.7.2, and try to say all dry and 
pre-action systems shall be galvanized!

Today is the day of those comments/questions!! Lmao

Thanks again!

Have a great weeekend!

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax - 631-580-1090


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John 
O'Connor
Sent: Friday, February 21, 2014 11:39 AM
To: [email protected]
Subject: RE: no dry type sprinkler systems allowed in light hazard applications

Forum,
How 'bout the thousands of nursing homes installed by this industry over the 
past 50 years? Most located north of I-10 have dry pipe systems protecting 
attic spaces with dry pendent heads below.  All light hazard.  How did that 
happen?  Have this AHJ produce chapter and verse.  Good luck.
John O'Connor
National Fire Sprinklers
Nashville 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Friday, February 21, 2014 9:23 AM
To: [email protected]
Subject: RE: no dry type sprinkler systems allowed in light hazard applications

There is an annex section discouraging dry in warm rooms.  Now I'd bet very few 
areas are cold and light hazard. Well except attics.  Ask how one does an 
attic. I wonder if they are linking cold is not light usually.  It's annex so 
don't think I'm agreeing just thinking of something out of the box.


Chris Cahill
Fire Protection Engineer
Burns & McDonnell
952-656-3652
[email protected]


-------- Original message --------
From: "Reed A. Roisum, C.E.T."
Date:02/21/2014 10:11 AM (GMT-05:00)
To: [email protected]
Subject: RE: no dry type sprinkler systems allowed in light hazard applications

Better ask the AHJ for chapter and verse on that one cuz I'm pretty sure that 
is not in there.

Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer 
| Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve 
Mackinnon
Sent: Friday, February 21, 2014 9:06 AM
To: [email protected]
Subject: no dry type sprinkler systems allowed in light hazard applications

Good morning all,

I have a Local AHJ that is saying in NFPA 13, 2007 edition it states that dry 
systems are not allowed in light hazard applications, does anyone have an idea 
of where this is located?? I've looked through the standard a few times and 
can't put my finger on anything close.

Thanks in advance

Steven

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax - 631-580-1090


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1432 / Virus Database: 3705/6613 - Release Date: 02/21/14

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to