Subject: Re: no dry type sprinkler systems allowed in light hazard applications

That is indeed accurate IF YOU ARE INSTALLING CMSA (aka large drop) sprinklers. 
 Also worth noting that the first draft is now available and that requirement 
was deleted from 8.4.7.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Feb 21, 2014, at 8:45 AM, Steve Mackinnon <[email protected]> wrote:

> Thank you guys for your input!! 
> 
> I just had another AHJ bring up section 8.4.7.2, and try to say all dry and 
> pre-action systems shall be galvanized!
> 
> Today is the day of those comments/questions!! Lmao
> 
> Thanks again!
> 
> Have a great weeekend!