Good to know, thank you. Steven MacKinnon Fire Protection Division Hartcorn Plumbing and Heating, Inc. 850 South Second Street Ronkonkoma, NY 11779 Office 631-580-2300 Fax - 631-580-1090
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Friday, February 21, 2014 2:45 PM To: [email protected] Subject: Re: no dry type sprinkler systems allowed in light hazard applications That is indeed accurate IF YOU ARE INSTALLING CMSA (aka large drop) sprinklers. Also worth noting that the first draft is now available and that requirement was deleted from 8.4.7. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Feb 21, 2014, at 8:45 AM, Steve Mackinnon <[email protected]> wrote: > Thank you guys for your input!! > > I just had another AHJ bring up section 8.4.7.2, and try to say all dry and > pre-action systems shall be galvanized! > > Today is the day of those comments/questions!! Lmao > > Thanks again! > > Have a great weeekend! _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org