Has the AHJ come back and told you to look it up yourself because you are the 
sprinkler expert? Seen that before. 

Put about 3 hours in this morning driving to a jobsite to inspect the 
installation of 6 heads below a new ceiling. Now I have to write an affidavit 
to say it was done correctly, which gets stamped and sent to the local FM 
before he will issue the CO. He has already inspected and approved it. Gotta 
love MA. Yes, this is another one of those days. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Feb 21, 2014, at 11:39 AM, "John O'Connor" <[email protected]> wrote:
> 
> Forum,
> How 'bout the thousands of nursing homes installed by this industry over the
> past 50 years? Most located north of I-10 have dry pipe systems protecting
> attic spaces with dry pendent heads below.  All light hazard.  How did that
> happen?  Have this AHJ produce chapter and verse.  Good luck.
> John O'Connor
> National Fire Sprinklers
> Nashville 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Cahill,
> Christopher
> Sent: Friday, February 21, 2014 9:23 AM
> To: [email protected]
> Subject: RE: no dry type sprinkler systems allowed in light hazard
> applications
> 
> There is an annex section discouraging dry in warm rooms.  Now I'd bet very
> few areas are cold and light hazard. Well except attics.  Ask how one does
> an attic. I wonder if they are linking cold is not light usually.  It's
> annex so don't think I'm agreeing just thinking of something out of the box.
> 
> 
> Chris Cahill
> Fire Protection Engineer
> Burns & McDonnell
> 952-656-3652
> [email protected]
> 
> 
> -------- Original message --------
> From: "Reed A. Roisum, C.E.T."
> Date:02/21/2014 10:11 AM (GMT-05:00)
> To: [email protected]
> Subject: RE: no dry type sprinkler systems allowed in light hazard
> applications
> 
> Better ask the AHJ for chapter and verse on that one cuz I'm pretty sure
> that is not in there.
> 
> Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection
> Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Mackinnon
> Sent: Friday, February 21, 2014 9:06 AM
> To: [email protected]
> Subject: no dry type sprinkler systems allowed in light hazard applications
> 
> Good morning all,
> 
> I have a Local AHJ that is saying in NFPA 13, 2007 edition it states that
> dry systems are not allowed in light hazard applications, does anyone have
> an idea of where this is located?? I've looked through the standard a few
> times and can't put my finger on anything close.
> 
> Thanks in advance
> 
> Steven
> 
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1432 / Virus Database: 3705/6613 - Release Date: 02/21/14
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to