7.3.2.1 is a good point, the ahj was more looking at office and combustible 
attic systems... I believe TYCO makes a dry system for residential 
applications. 

Thanks
Steven 

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax - 631-580-1090


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland 
Huggins
Sent: Friday, February 21, 2014 3:31 PM
To: [email protected]
Subject: Re: no dry type sprinkler systems allowed in light hazard applications

Look at section 7.3.2.1. (2007 ed)  It states that dry pipe systems protecting 
dwelling units can not use the options in 7.2.3.3 (no time limit of water 
delivery when capacity is less than 500 gal) or 7.2.3.4 (no time limit of water 
delivery when capacity is less than 750 gal and a QOD is installed).

This is not a residential sprinkler issue but a dwelling unit issue even with 
spray sprinklers.  This is the only restriction for a light hazard occupancy.  
Residential sprinkler can be part of a dry pipe system (the 15 sec is part of 
their listing and reasonable to assume their is a correlation well maybe better 
to say this was the source of the general requirement)

This was further restricted in 2010 ed within the Calculated Timed option in 
7.2.3.6 but saying water delivery must be with 15 seconds.  Technically the was 
applicable only if you applied this option.

This was better clarified in the 2013 ed where the option to apply the 60 sec 
rule was removed (for dwelling units) and the 15 sec water delivery requirement 
was moved to 7.2.3.1.1 as a general requirement.

Bottom line, the standard states the system shall be wet pipe only in ch 12 - 
Storage and granted that 8.16.4.1.1 implies the same requirement by saying when 
subject to freezing it shall be a dry-pipe system.  Actually it's not an 
exception to wet pipe but a requirement for freezing conditions so no 
restriction there for normal conditions. So without there being something else 
that I can't remember (a distinct possibility) nor find, there is nothing that 
forbids dry pipe in light hazard occupancies but the text for a subset of LH 
supports it use in all LH occupancies.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Feb 21, 2014, at 7:05 AM, Steve Mackinnon <[email protected]> wrote:

> Good morning all,
> 
> I have a Local AHJ that is saying in NFPA 13, 2007 edition it states that dry 
> systems are not allowed in light hazard applications, does anyone have an 
> idea of where this is located?? I've looked through the standard a few times 
> and can't put my finger on anything close.
> 
> Thanks in advance
> 
> Steven
> 
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to