This one has me stumped for some reason. Do I need heads in this combustible 
concealed floor/ceiling space?
 
Floor on top is plywood attached to 11 1/2" deep open web wood floor joists 
that are completely filled with insulation, then a 3" air gap, then 2x6 ceiling 
joists with drywall ceiling attached to the bottom. So it is 1'-8" from the 
bottom of the plywood to the top of the drywall, with the top 11 1/2' full of 
insulation.
 
Greg Lindholm
Fire Protection Project Manager
Howe Heating & Plumbing, Inc.
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to