I'd say no. There is only about 3" clear between the bottom and top of the
framing. See figure 8.6.4.1.5.1 ('13).
Ron F
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gregory
Lindholm
Sent: Wednesday, February 26, 2014 9:05 AM
To: SprinklerFORUM
Subject: Combustible Concealed Space
This one has me stumped for some reason. Do I need heads in this combustible
concealed floor/ceiling space?
Floor on top is plywood attached to 11 1/2" deep open web wood floor joists
that are completely filled with insulation, then a 3" air gap, then 2x6 ceiling
joists with drywall ceiling attached to the bottom. So it is 1'-8" from the
bottom of the plywood to the top of the drywall, with the top 11 1/2' full of
insulation.
Greg Lindholm
Fire Protection Project Manager