> I'd say no. There is only about 3" clear between the bottom and top of the
> framing. See figure 8.6.4.1.5.1 ('13).
> Ron F
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Gregory
> Lindholm
> Sent: Wednesday, February 26, 2014 9:05 AM
> To: SprinklerFORUM
> Subject: Combustible Concealed Space
>
> This one has me stumped for some reason. Do I need heads in this combustible
> concealed floor/ceiling space?
>
> Floor on top is plywood attached to 11 1/2" deep open web wood floor joists
> that are completely filled with insulation, then a 3" air gap, then 2x6
> ceiling joists with drywall ceiling attached to the bottom. So it is 1'-8"
> from the bottom of the plywood to the top of the drywall, with the top 11
> 1/2' full of insulation.
>
> Greg Lindholm