NFPA 1 - 13.2.2.2

Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



Celebrating over 34 years of life safety


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Tuesday, March 11, 2014 1:09 PM
To: [email protected]
Subject: Standpipe requirement

I thought that if I have a 4 story OR the elevation of the highest floor is 30' 
above or below the fd vehicle access I would need a standpipe. When I look at 
2009 IBC section 905.3.1 it only references the 30'. So I have a 4 story 
apartment where the top floor is right at 30'- it doesn't look like I need a 
standpipe. I just had it in my mind that once I hit 4 stories it was a done 
deal. These are design build apartment complexes with S2 Parking garage below 
where the architect is considering IIIA, IIIB or VB and I am looking at the 
different sprinkler options for each. Looks like I can have a 13R in the 
residential floors in IIIA where the other options are 13 throughout.  Is there 
another section that kicks it in at a 4th floor? Maybe that was old UBC or 
maybe I dreamed it up.

905.3.1 Height. Class III standpipe systems shall be installed throughout 
buildings where the floor level of the highest story is located more than 30 
feet (9144 mm) above the lowest level of fire department vehicle access, or 
where the floor level of the lowest story is located more than 30 feet (9144 
mm) below the highest level of fire department vehicle access.

Another thing I will throw out there that it looks like I had wrong... I 
thought the fire flow reduction was only available for 903.3.1.1 (13 system) 
but when I look at IFC section B105.2 - exception- It clearly allows it for 
903.1.2 as well. Probably common knowledge for most of you but fyi...



Rod at Rapid


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to