Rod, here ya go....

2009 IBC 905.3.1 Height. 

Class III standpipe systems shall be installed throughout buildings WHERE
THE FLOOR LEVEL OF THE HIGHEST STORY is located MORE THAN 30 FEET (9144 MM)
ABOVE THE LOWEST LEVEL OF FIRE DEPARTMENT VEHICLE ACCESS, or where the floor
level of the lowest story is located more than 30 feet (9144 mm) below the
highest level of fire department vehicle access.

Exceptions: 1. Class I standpipes are allowed in buildings equipped
throughout with an automatic sprinkler system in accordance with Section
903.3.1.1 (13) OR 903.3.1.2.(13R)

Hope that helps,

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Tuesday, March 11, 2014 1:09 PM
To: [email protected]
Subject: Standpipe requirement

I thought that if I have a 4 story OR the elevation of the highest floor is
30' above or below the fd vehicle access I would need a standpipe. When I
look at 2009 IBC section 905.3.1 it only references the 30'. So I have a 4
story apartment where the top floor is right at 30'- it doesn't look like I
need a standpipe. I just had it in my mind that once I hit 4 stories it was
a done deal. These are design build apartment complexes with S2 Parking
garage below where the architect is considering IIIA, IIIB or VB and I am
looking at the different sprinkler options for each. Looks like I can have a
13R in the residential floors in IIIA where the other options are 13
throughout.  Is there another section that kicks it in at a 4th floor? Maybe
that was old UBC or maybe I dreamed it up.

905.3.1 Height. Class III standpipe systems shall be installed throughout
buildings where the floor level of the highest story is located more than 30
feet (9144 mm) above the lowest level of fire department vehicle access, or
where the floor level of the lowest story is located more than 30 feet (9144
mm) below the highest level of fire department vehicle access.

Another thing I will throw out there that it looks like I had wrong... I
thought the fire flow reduction was only available for 903.3.1.1 (13 system)
but when I look at IFC section B105.2 - exception- It clearly allows it for
903.1.2 as well. Probably common knowledge for most of you but fyi...



Rod at Rapid


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to