I would at a minimum speak with the local AHJ, as they may require a permit.
If you intend to replace all of the piping with plastic, the AHJ may not permit the use of antifreeze in this new system.
Is this a residential system?


On 8/8/2014 4:40 PM, Brad Casterline wrote:
It just occurred to me though Douglas (on a smoke break as usual) I would be
worried that the existing pipe size is per code, so I would calc it anyway.

-----Original Message-----
From: Brad Casterline [mailto:[email protected]]
Sent: Friday, August 08, 2014 3:30 PM
To: [email protected]
Subject: RE: copper pipe vs CPVC

Both C=150 and the best part is it looks like the I.D of CPVC is bigger than
type K,L, and M copper.

Brad

-----Original Message-----
From: Douglas Hicks [mailto:[email protected]]
Sent: Friday, August 08, 2014 1:41 PM
To: [email protected]
Subject: copper pipe vs CPVC

One of our group homes has leaking copper pipe.  The owner told me their
experience is to replace the copper with CPVC.  I like that, faster and
easier for us.  But, do I need to get the system re-engineered when changing
to CPVC?  Can I just replace size for like size?

The system is 20+ years old so I am going to propose new sprinklers.
Besides, some of the heads are corroded and some have paint on them.
We will also provide a means to test the antifreeze, at present there is no
way to test the solution.

I  am going to exclude sheet rock and painting from the job.

Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


--
Forest Wilson
Project Manager
193 California St
Xenia OH 45385
Ph: 937-736-0425

///WHO IS JOHN GALT?///

******This email and any files transmitted with it are confidential and 
intended solely for the use of the individual or entity to whom they are 
addressed. If you have received this email in error please notify the system 
manager. This message contains confidential information and is intended only 
for the individual named. If you are not the named addressee you should not 
disseminate, distribute or copy this e-mail. Please notify the sender 
immediately by e-mail if you have received this e-mail by mistake and delete 
this e-mail from your system. If you are not the intended recipient you are 
notified that disclosing, copying, distributing or taking any action in 
reliance on the contents of this information is strictly prohibited.***

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to