The customer wants the copper replaced with CPVC


-----Original Message----- From: Duane Johnson
Sent: Monday, August 11, 2014 5:17 AM
To: [email protected]
Subject: RE: copper pipe vs CPVC

Your statement earlier holds true only if portions of the system are being replaced. I was under the assumption the entire system was being replaced, in which increasing diameter will not be more demanding.

And yes, there is more to calcs...

Duane

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of Matthew Willis
Sent: Monday, August 11, 2014 7:32 AM
To: [email protected]
Subject: RE: copper pipe vs CPVC

There is more to a calc than just pressure. Flow is also part. Why do you think we are required to pick the sprinkler closer to the main on a tree calc?
R/
Matt
On Aug 11, 2014 7:23 AM, "Duane Johnson" <[email protected]>
wrote:

No, no, no.  As long as you are increasing the ID along the primary
path, you are not making the calc more demanding. Increasing the ID
reduces the friction loss per ft. and reduces the overall required
pressure of the system.

Duane


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to