Then the answer to your original question, in my opinion, is yes, you must
re-engineer. Not only is the pipe not the same size, but the hangers are
different as well. With CPVC being in a freezing environment, the temps in
the attic normally vary. This means required expansion loops in the system
for long runs. Especially if AF is involved. I cannot see a "like for like"
at any level.
I also agree with Mark that you should find the problem first. It may not
be what you think. Replacing the system might turn into treating the
symptom, not the problem.

R/
Matt


On Mon, Aug 11, 2014 at 9:03 AM, Douglas Hicks <[email protected]> wrote:

>
> The customer wants the copper replaced with CPVC
>
>
> -----Original Message----- From: Duane Johnson
> Sent: Monday, August 11, 2014 5:17 AM
> To: [email protected]
> Subject: RE: copper pipe vs CPVC
>
> Your statement earlier holds true only if portions of the system are being
> replaced. I was under the assumption the entire system was being replaced,
> in which increasing diameter will not be more demanding.
>
> And yes, there is more to calcs...
>
> Duane
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected].
> org] On Behalf Of Matthew Willis
> Sent: Monday, August 11, 2014 7:32 AM
> To: [email protected]
> Subject: RE: copper pipe vs CPVC
>
> There is more to a calc than just pressure. Flow is also part. Why do you
> think we are required to pick the sprinkler closer to the main on a tree
> calc?
> R/
> Matt
> On Aug 11, 2014 7:23 AM, "Duane Johnson" <[email protected]>
> wrote:
>
>  No, no, no.  As long as you are increasing the ID along the primary
>> path, you are not making the calc more demanding. Increasing the ID
>> reduces the friction loss per ft. and reduces the overall required
>> pressure of the system.
>>
>> Duane
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>