That is the point, increasing the pipe size does not necessarily increase the 
required flow. If you are changing only portions of the system, it will depend 
on which segment you are changing among other factors, such as velocity.

However, if you are increasing the ID to every segment in your system, the 
overall effect will be a less demanding system. This is inherent in the 
Hazen-Williams formula...p=(4.52*Q^1.85)/(C^1.85*d^4.87). Yes, increasing Q 
will increase the friction loss in a pipe. But, increasing diameter will 
decrease the friction loss in a pipe because d is in the denominator. More 
importantly, d is raised to the 4.87 while Q is only raised to the 1.85. So, 
even if Q is increased slightly, increasing the d will have the larger effect. 
In this case (a one for one replacement throughout), increasing the ID will 
reduce the friction loss and in turn reduce the overall pressure requirement.

Try it. If you have AutoSprink, use the Wizard to create a tree system...just 
click next until it is finished (the parameters don't matter at this point). 
Then, start changing the IDs. Remember to keep the C factor constant (cuz in 
this example it does not change). If you are using HASS, take one of your old 
calcs and replace your existing sch 40 branchlines with sch 10. Your calc will 
be less demanding. :)

Duane

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew Willis
Sent: Monday, August 11, 2014 9:53 AM
To: [email protected]
Subject: Re: copper pipe vs CPVC

So if increasing the pipe changes the required flow from 100gpm to 200gpm due 
to the larger size, you do not think this is more demanding?
Would you please change subject line for me/us as gmail is showing it's butt. 
Thanks,

Matt


On Mon, Aug 11, 2014 at 8:17 AM, Duane Johnson <[email protected]>
wrote:

> Your statement earlier holds true only if portions of the system are 
> being replaced. I was under the assumption the entire system was being 
> replaced, in which increasing diameter will not be more demanding.
>
> And yes, there is more to calcs...
>
> Duane
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Matthew 
> Willis
> Sent: Monday, August 11, 2014 7:32 AM
> To: [email protected]
> Subject: RE: copper pipe vs CPVC
>
> There is more to a calc than just pressure. Flow is also part. Why do 
> you think we are required to pick the sprinkler closer to the main on 
> a tree calc?
> R/
> Matt
> On Aug 11, 2014 7:23 AM, "Duane Johnson" <[email protected]>
> wrote:
>
> > No, no, no.  As long as you are increasing the ID along the primary 
> > path, you are not making the calc more demanding. Increasing the ID 
> > reduces the friction loss per ft. and reduces the overall required 
> > pressure of the system.
> >
> > Duane
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of Matthew 
> > Willis
> > Sent: Friday, August 08, 2014 7:54 PM
> > To: [email protected]
> > Subject: Re: copper pipe vs CPVC
> >
> > Especially since the I.D. like you said is larger. This often = more 
> > demanding. Bigger is not always better.
> >
> > R/
> > Matt
> >
> >
> > On Fri, Aug 8, 2014 at 4:40 PM, Brad Casterline 
> > <[email protected]>
> > wrote:
> >
> > > It just occurred to me though Douglas (on a smoke break as usual) 
> > > I would be worried that the existing pipe size is per code, so I 
> > > would calc it anyway.
> > >
> > > -----Original Message-----
> > > From: Brad Casterline [mailto:[email protected]]
> > > Sent: Friday, August 08, 2014 3:30 PM
> > > To: [email protected]
> > > Subject: RE: copper pipe vs CPVC
> > >
> > > Both C=150 and the best part is it looks like the I.D of CPVC is 
> > > bigger than type K,L, and M copper.
> > >
> > > Brad
> > >
> > > -----Original Message-----
> > > From: Douglas Hicks [mailto:[email protected]]
> > > Sent: Friday, August 08, 2014 1:41 PM
> > > To: [email protected]
> > > Subject: copper pipe vs CPVC
> > >
> > > One of our group homes has leaking copper pipe.  The owner told me 
> > > their experience is to replace the copper with CPVC.  I like that, 
> > > faster and easier for us.  But, do I need to get the system 
> > > re-engineered when changing to CPVC?  Can I just replace size for 
> > > like size?
> > >
> > > The system is 20+ years old so I am going to propose new sprinklers.
> > > Besides, some of the heads are corroded and some have paint on them.
> > > We will also provide a means to test the antifreeze, at present 
> > > there is no way to test the solution.
> > >
> > > I  am going to exclude sheet rock and painting from the job.
> > >
> > > Douglas Hicks
> > > General Fire Equipment Co of Eastern Oregon, Inc 
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
> > > in
> > > kl
> > > er.org
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
> > > in
> > > kl
> > > er.org
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
> > > in
> > > kl
> > > er.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to