Keep in mind that NFPA Standards are not the only driving documents.   The 
Building, Fire, Mechanical, Plumbing Codes provide the directives of what is 
required.  The NFPA Standards then give the direction on how to apply the 
requirement to the specific conditions.  

For installations which are built in accordance with the International Code 
Council (ICC) set of codes, the type of duct system required is driven by the 
International Mechanical Code (IMC).  

The International Mechanical Code, Chapter 5, Section 506 provides direction on 
the type of material for grease ducts serving Type I commercial kitchen hoods.  
 

But, if you are not required to follow the International Code Council codes, 
you need to find out what is the applicable and enforced local code and start 
there for direction.


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Phong - Indochine Engineering
Sent: Monday, August 18, 2014 9:42 PM
To: [email protected]
Subject: Material for kitchen duct of hotel restaurant

Dear All,

This is not a real question for sprinkler but am appreciated if you can help. 
Is there a requirement in NFPA that the ductwork for kitchen of a hotel 
restaurant (commercial kitchen, not residential) must be stainless steel? Seems 
NFPA90A do not.

NFPA90A:

2-3 Air Distribution. 
2-3.1 Air Ducts.
2-3.1.1 Air ducts shall be permitted to be rigid or flexible and shall be 
constructed of materials that are reinforced and sealed to satisfy the 
requirements for the use of the air duct system, such as the supply air system, 
the return or exhaust air system, and the variable volume/pressure air system.
2-3.1.2 Air ducts shall be constructed of the following materials:
(1) Iron, steel, aluminum, copper, concrete, masonry, or clay tile.
(2) Class 0 or Class 1 rigid or flexible air ducts tested in accordance with UL 
181,  Standard for Safety Factory-Made Air Ducts and Air Connectors, and 
installed in conformance with the conditions of listing.


Regards,
Le Vu Phong
Mobile:  +84 (0) 902 363 525
                      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to