Keep in mind that NFPA Standards are not the only driving documents. The Building, Fire, Mechanical, Plumbing Codes provide the directives of what is required. The NFPA Standards then give the direction on how to apply the requirement to the specific conditions.
For installations which are built in accordance with the International Code Council (ICC) set of codes, the type of duct system required is driven by the International Mechanical Code (IMC). The International Mechanical Code, Chapter 5, Section 506 provides direction on the type of material for grease ducts serving Type I commercial kitchen hoods. But, if you are not required to follow the International Code Council codes, you need to find out what is the applicable and enforced local code and start there for direction. Craig L. Prahl Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Phong - Indochine Engineering Sent: Monday, August 18, 2014 9:42 PM To: [email protected] Subject: Material for kitchen duct of hotel restaurant Dear All, This is not a real question for sprinkler but am appreciated if you can help. Is there a requirement in NFPA that the ductwork for kitchen of a hotel restaurant (commercial kitchen, not residential) must be stainless steel? Seems NFPA90A do not. NFPA90A: 2-3 Air Distribution. 2-3.1 Air Ducts. 2-3.1.1 Air ducts shall be permitted to be rigid or flexible and shall be constructed of materials that are reinforced and sealed to satisfy the requirements for the use of the air duct system, such as the supply air system, the return or exhaust air system, and the variable volume/pressure air system. 2-3.1.2 Air ducts shall be constructed of the following materials: (1) Iron, steel, aluminum, copper, concrete, masonry, or clay tile. (2) Class 0 or Class 1 rigid or flexible air ducts tested in accordance with UL 181, Standard for Safety Factory-Made Air Ducts and Air Connectors, and installed in conformance with the conditions of listing. Regards, Le Vu Phong Mobile: +84 (0) 902 363 525 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org