> Has the water supply to the pump been tested and deemed sufficient and 
> meeting the original design criteria?
> 
> Craig L. Prahl 
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Todd - Work
> Sent: Wednesday, November 12, 2014 2:43 PM
> To: [email protected]
> Subject: Re: pump replacement issue
> 
> The manufacturer's literature states that this pump requires a minimum of 
> 22.1 hp to meet the demand. I have no idea what the actual output of the pump 
> is but the plate says 30 hp. Not sure if torque would play into this at all.
> 
> My contract was only to witness the pump test and write a letter regarding 
> it. Determining if it provided sufficient water for the sprinklers was not a 
> part of it. At the beginning of this project, I submitted a proposal through 
> the contractor to analyze the sprinkler systems (two separate schools) and 
> make sure the new pumps met the criteria, but that was turned down as not 
> needed. I have some issues with the system in at least one school, but that 
> is well documented. 
> 
> The test was done using 2 Hosemonsters with 1-3/4" inserts. When the straight 
> 2-1/2" HM's were used, the pressure dropped to 4 psi, which is below the 
> minimum HM recommends. 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
> 
>> On Nov 12, 2014, at 8:23 AM, Matt Grise <[email protected]> wrote:
>> 
>> It is still early for me - so I cannot guarantee 100% brain power behind 
>> this...
>> 
>> I would say that the HP deficit could definitely cause your flow 
>> shortage. The work that the motor puts in results in water flow and 
>> water pressure. You can get more flow OR more pressure for the same 
>> HP, but if you want more of both it takes more power. (for a fun time, 
>> read that sentence with Mr Scotty's voice when captain Kirk asks for 
>> warp 7)
>> 
>> Also - lots of pump literature will also include a horsepower demand curve 
>> under the pressure/flow curve. If it is there, you might line up 30 hp 
>> against th