Neither.  It's the flow you need for a building. You might get it from a muni 
or private. Absolutely nothing to do with sprinklers except you get a reduction 
if building is sprinklered.


Chris Cahill
Fire Protection Engineer
Burns & McDonnell
952-656-3652
[email protected]


-------- Original message --------
From: [email protected]
Date:12/05/2014 8:12 PM (GMT-06:00)
To: [email protected]
Subject: A Poll of the Experienced

Over this weekend I'd like to ask the opinion of those forumites experienced in 
the reading and understanding of the "International Fire  Code" on the topic of 
"Fire Flow" described in Chapter 5, and further prescribed in Appendix B. Is 
the available flow rate and residual pressure referenced, intended to describe 
these values of the municipal or private water supply available to the building 
site? Or, the minimum output of any fire pump associated specifically with the 
automatic sprinkler system in the building?
Any takers? Questions? Clarifications?
Thanks for any answers.