It does supply the sprinkler systems through the site fireline. It has a full 
size bypass around the fire pump. In addition the site fireline has a second 
connection directly to the city water system via a backflow device. 

Mark at Aero
602 820-7894

Sent from my iPhone

> On Dec 5, 2014, at 9:06 PM, "Travis Mack" <[email protected]> wrote:
> 
> Does the fire pump supply the site hydrants? Site fire flow and fire 
> sprinkler demand are two independent entities. 
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
> 
> Sent from my iPhone
> 
>> On Dec 5, 2014, at 7:29 PM, <[email protected]> <[email protected]> 
>> wrote:
>> 
>> I think I agree with you, but to be very specific, let's assume I'm 
>> designing a new building on a greenfield site which is served by a public 
>> water system. The building is type V construction, 600,000 square feet and 
>> fully protected with ESFR sprinklers. Table B105.2 indicated a fire flow 
>> rate of 8000 GPM, reduced to 4000 GPM for sprinkler credit, at minimum 
>> 20psi. My question is, WHERE is this 4000 GPM at 20 psi measured? At the 
>> city water main connection? Or at the fire pump discharge? 
>> 
>> Mark at Aero
>> 602 820-7894
>> 
>> Sent from my iPhone
>> 
>>> On Dec 5, 2014, at 7:17 PM, "Cahill, Christopher" <[email protected]> 
>>> wrote:
>>> 
>>> Neither.  It's the flow you need for a building. You might get it from a 
>>> muni or private. Absolutely nothing to do with sprinklers except you get a 
>>> reduction if building is sprinklered.
>>> 
>>> 
>>> Chris Cahill
>>> Fire Protection Engineer
>>> Burns & McDonnell
>>> 952-656-3652
>>> [email protected]
>>> 
>>> 
>>> -------- Original message --------
>>> From: [email protected]
>>> Date:12/05/2014 8:12 PM (GMT-06:00)
>>> To: [email protected]
>>> Subject: A Poll of the Experienced
>>> 
>>> Over this weekend I'd like to ask the opinion of those forumites 
>>> experienced in the reading and understanding of the "International Fire  
>>> Code" on the topic of "Fire Flow" described in Chapter 5, and further 
>>> prescribed in Appendix B. Is the available flow rate and residual pressure 
>>> referenced, intended to describe these values of the municipal or private 
>>> water supply available to the building site? Or, the minimum output of any 
>>> fire pump associated specifically with the automatic sprinkler system in 
>>> the building?
>>> Any takers? Questions? Clarifications?
>>> Thanks for any answers.
>>> 
>>> Mark at Aero
>>> 602 820-7894
>>> 
>>> Sent from my iPhone
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to