Without looking it up, my educated guess is annually. Sent from my iPhone
> On Dec 20, 2014, at 6:59 PM, "Jody Massey" <[email protected]> > wrote: > > I know that this is probably a stupid question... > > I know that NFPA requires the following, but is it part of the annual or 5 > year inspection? In other words, do I need to review this myself > separately. > > Per NFPA-25, 2011, section 5.3.1.1.1 if sprinklers are 50 years old they > shall be replaced or have a representative sample tested. They must be > tested every 10 years after that. > 5.3.1.1.2 states if the sprinklers were manufactured prior to 1920 they > shall be replaced. > 5.3.1.1.1.3 states if they are quick response heads, after 20 years they > must be replaced or have a sample tested. > > I just need to be sure. Thank you or your insight. > ᐧ > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org