> I know that NFPA requires the following, but is it part of the annual or 5
> year inspection? In other words, do I need to review this myself
> separately.
> 
> Per NFPA-25, 2011, section 5.3.1.1.1 if sprinklers are 50 years old they
> shall be replaced or have a representative sample tested. They must be
> tested every 10 years after that.
> 5.3.1.1.2 states if the sprinklers were manufactured prior to 1920 they
> shall be replaced.
> 5.3.1.1.1.3 states if they are quick response heads, after 20 years they
> must be replaced or have a sample tested.
> 
> I just need to be sure. Thank you or your insight.