QR has an FR element. But FR can also equal RES. FR can also equal extended 
coverage standard response or even ESFR. In other words there are many 
sprinkler types that have fast response elements. 

Duane Johnson 
Strickland Fire Protection
Sent from my iPhone

> On Dec 22, 2014, at 6:18 PM, Jeff Bridges <[email protected]> wrote:
> 
> One additional question also-
> IS it QR or FR heads that need to be tested at 20 years/ every 10 thereafter?
> Section 5.1.1.1.3 says fast response elements.
> Maybe I'm missing something?
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Roland Huggins
> Sent: Monday, December 22, 2014 7:55 AM
> To: [email protected]
> Subject: Re: Do normal yearly fire sprinkler inspections review for older 
> heads?
> 
> It’s NOT part of the annual or the 5 yr.  IT is part of the 20 yr for QR and 
> 50 yr for SR.  Technically there is no such thing as an annual inspection per 
> NFPA 25.  There are items with an annual frequency but it’s not uncommon to 
> check all items with a frequency up to 1 yr during that inspection.   Having 
> said that, we had it as part of our old 5 year form just to ensure it was 
> recorded somewhere.  It gets an N/A util the system is older.
> 
> Roland
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
> 
> 
> 
> 
> 
>> On Dec 20, 2014, at 4:02 PM, Jody Massey <[email protected]> 
>> wrote:
>> 
>> I know that this is probably a stupid question...
>> 
>> I know that NFPA requires the following, but is it part of the annual 
>> or 5 year inspection? In other words, do I need to review this myself 
>> separately.
>> 
>> Per NFPA-25, 2011, section 5.3.1.1.1 if sprinklers are 50 years old 
>> they shall be replaced or have a representative sample tested. They 
>> must be tested every 10 years after that.
>> 5.3.1.1.2 states if the sprinklers were manufactured prior to 1920 
>> they shall be replaced.
>> 5.3.1.1.1.3 states if they are quick response heads, after 20 years 
>> they must be replaced or have a sample tested.
>> 
>> I just need to be sure. Thank you or your insight.
>> ᐧ
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to