Interesting- State of California requires Annual inspections. If there is technically no annual inspection then who would perform those activities required annually? I would fall over dead if a building owner actually ever looked into the copy of NFPA 235 we leave with the system. We all know within 12 months no one can find an as-built plan much less a maintenance manual
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Monday, December 22, 2014 7:55 AM To: [email protected] Subject: Re: Do normal yearly fire sprinkler inspections review for older heads? It’s NOT part of the annual or the 5 yr. IT is part of the 20 yr for QR and 50 yr for SR. Technically there is no such thing as an annual inspection per NFPA 25. There are items with an annual frequency but it’s not uncommon to check all items with a frequency up to 1 yr during that inspection. Having said that, we had it as part of our old 5 year form just to ensure it was recorded somewhere. It gets an N/A util the system is older. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Dec 20, 2014, at 4:02 PM, Jody Massey <[email protected]> > wrote: > > I know that this is probably a stupid question... > > I know that NFPA requires the following, but is it part of the annual > or 5 year inspection? In other words, do I need to review this myself > separately. > > Per NFPA-25, 2011, section 5.3.1.1.1 if sprinklers are 50 years old > they shall be replaced or have a representative sample tested. They > must be tested every 10 years after that. > 5.3.1.1.2 states if the sprinklers were manufactured prior to 1920 > they shall be replaced. > 5.3.1.1.1.3 states if they are quick response heads, after 20 years > they must be replaced or have a sample tested. > > I just need to be sure. Thank you or your insight. > ᐧ > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org