No. Don’t believe that 140 deg. number. You cannot use the “normal” operating 
condition, if that is where the 140 is coming from. Depending on what this 
heating design is for it is likely not controlled by a space temperature 
sensor. In other words there could be nothing local to the panel that might 
limit the water temperature. The system will probably be either on or off 
operating at whatever water temperature the heating component happens to be 
capable of putting out, which could easily be way, way off the mark due to any 
number of screwup reasons, including running during summer. The problem would 
not be so bad if the heater were a Mr. Coffee hundreds of feet away, but it 
might be a monster in the next room. Maybe this is solar with some booster. 
Question the entire system. The designers and manufacturer reps will often say, 
“that could never happen” without being able to explain why that would be in 
terms that make physical sense. Do an age check and ask yourself how would they 
possibly know for sure. Have someone put it in writing what a reasonable 
determination for the maximum temperatures that might occur. You will still 
need to make an assessment based on the space conditions. It sounds like you 
are doing this. The concern might not be so bad if this is a overhang condition 
open to the outside but this might be an enclosed space or a public assembly 
space where the owner might crank up the heat to keep the clients at the space. 
      

Sorry but I do not think it would be right to volunteer any temperature or 
distance numbers other that saying stick at least to the 50 degree rule.

Allan Seidel
St. Louis, MO


> On Mar 10, 2015, at 6:29 PM, Jerry Van Kolken <[email protected]> wrote:
> 
> Has anyone dealt with Radiant Heat Panels in the ceiling?
> 
> 
> 
> I have project that will be using these panels with a water temperature feed
> of 140 deg. The panel will be putting out 124 BTUs. But I don't know how to
> translate that information into a safe distance or temp for the sprinkler
> be.
> 
> 
> 
> Any info is appreciated. 
> 
> 
> 
> Jerry Van Kolken
> 
> Millennium Fire Protection Corp.
> 
> 101 Copperwood Way, Suite H
> 
> Oceanside, CA 92058
> 
> (760) 722-2722 FX 722-2730
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to