I will question the 124 BTU's, assuming it is BTU/hour, which works out to 
about 37 watts, which is very small. Could it be BTU/Hr per linear foot maybe? 
In the past I have located sprinklers using the requirement for hot air 
diffusers. But it would be safer to find out the temperature at the panel and 
use a minimum safety of 50 deg.F. 

Tony 

----- Original Message -----

From: "Jerry Van Kolken" <[email protected]> 
To: [email protected] 
Sent: Tuesday, March 10, 2015 5:29:49 PM 
Subject: Spacing to a Radiant Heat Panel 

Has anyone dealt with Radiant Heat Panels in the ceiling? 



I have project that will be using these panels with a water temperature feed 
of 140 deg. The panel will be putting out 124 BTUs. But I don't know how to 
translate that information into a safe distance or temp for the sprinkler 
be. 



Any info is appreciated. 