In that case, I would try putting a thermometer at the desired distance and seeing how hot it gets (maybe setting up some sort of test area).
As Roland mentioned - the actual temperature that the head experiences could vary quite a lot, and it would be hard to get an accurate calculation. Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Wednesday, March 11, 2015 12:37 PM To: [email protected] Subject: RE: Spacing to a Radiant Heat Panel Matt, Thanks, I didn't consider that. But for conversation sake, let's say that the style the customer is requesting only comes in ordinary temp (i.e. flat plate residential concealer) Tony / Allen, I'm not familiar with the 50 deg rule you guys are referent to, could you explain. Thanks Jerry Van Kolken Millennium Fire Protection (760) 722-2722 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Matt Grise Sent: Wednesday, March 11, 2015 10:02 AM To: [email protected] Subject: RE: Spacing to a Radiant Heat Panel If the water comes in at 140, and intermediate temperature heads are ok to a max ceiling temperature of 150 - is there any reason that you could not just use intermediate temperature heads and then not worry about it? It seems like the max temperature of the panels would be 140 degrees (F?). Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Wednesday, March 11, 2015 11:58 AM To: [email protected] Subject: Re: Spacing to a Radiant Heat Panel The separation from the diffuser is based on heat transfer by convection. This is a radiation problem. The equation is easy enough but defining the coefficient is the great unknown. Does FM had any guidance? Wish I had a better answer for you. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Mar 10, 2015, at 9:14 PM, Tony Silva <[email protected]> wrote: > > I will question the 124 BTU's, assuming it is BTU/hour, which works > out to about 37 watts, which is very small. Could it be BTU/Hr per linear foot maybe? In the past I have located sprinklers using the requirement for hot air diffusers. But it would be safer to find out the temperature at the panel and use a minimum safety of 50 deg.F. > > Tony > > ----- Original Message ----- > > From: "Jerry Van Kolken" <[email protected]> > To: [email protected] > Sent: Tuesday, March 10, 2015 5:29:49 PM > Subject: Spacing to a Radiant Heat Panel > > Has anyone dealt with Radiant Heat Panels in the ceiling? > > > > I have project that will be using these panels with a water > temperature feed of 140 deg. The panel will be putting out 124 BTUs. > But I don't know how to translate that information into a safe > distance or temp for the sprinkler be. > > > > Any info is appreciated. > > > > Jerry Van Kolken > > Millennium Fire Protection Corp. > > 101 Copperwood Way, Suite H > > Oceanside, CA 92058 > > (760) 722-2722 FX 722-2730 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org