It comes from observing there is a 50 deg F difference between the maximum 
ceiling temperature and the middle of the temperature classification range that 
is appropriate for the maximum ceiling temperature. 


> On Mar 11, 2015, at 12:37 PM, Jerry Van Kolken <[email protected]> wrote:
> 
> Matt, 
> 
> Thanks, I didn't consider that.  But for conversation sake, let's say that
> the style the customer is requesting only comes in ordinary temp (i.e. flat
> plate residential concealer)
> 
>  Tony / Allen,
> 
> I'm not familiar with the 50 deg rule you guys are referent to, could you
> explain.
> 
> Thanks
> 
> Jerry Van Kolken
> Millennium Fire Protection
> (760) 722-2722
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Matt Grise
> Sent: Wednesday, March 11, 2015 10:02 AM
> To: [email protected]
> Subject: RE: Spacing to a Radiant Heat Panel
> 
> If the water comes in at 140, and intermediate temperature heads are ok to a
> max ceiling temperature of 150  - is there any reason that you could not
> just use intermediate temperature heads and then not worry about it? It
> seems like the max temperature of the panels would be 140 degrees (F?).
> 
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
> 
> *Licensed in KS & MO 
>  
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com 
>  
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Roland Huggins
> Sent: Wednesday, March 11, 2015 11:58 AM
> To: [email protected]
> Subject: Re: Spacing to a Radiant Heat Panel
> 
> The separation from the diffuser is based on heat transfer by convection.
> This is a radiation problem.  The equation is easy enough but defining the
> coefficient is the great unknown.  Does FM had any guidance?   Wish I had a
> better answer for you.
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
> 
> 
> 
> 
> 
>> On Mar 10, 2015, at 9:14 PM, Tony Silva <[email protected]> wrote:
>> 
>> I will question the 124 BTU's, assuming it is BTU/hour, which works out to
> about 37 watts, which is very small. Could it be BTU/Hr per linear foot
> maybe? In the past I have located sprinklers using the requirement for hot
> air diffusers. But it would be safer to find out the temperature at the
> panel and use a minimum safety of 50 deg.F. 
>> 
>> Tony
>> 
>> ----- Original Message -----
>> 
>> From: "Jerry Van Kolken" <[email protected]>
>> To: [email protected]
>> Sent: Tuesday, March 10, 2015 5:29:49 PM
>> Subject: Spacing to a Radiant Heat Panel
>> 
>> Has anyone dealt with Radiant Heat Panels in the ceiling? 
>> 
>> 
>> 
>> I have project that will be using these panels with a water 
>> temperature feed of 140 deg. The panel will be putting out 124 BTUs.
>> But I don't know how to translate that information into a safe 
>> distance or temp for the sprinkler be.
>> 
>> 
>> 
>> Any info is appreciated. 
>> 
>> 
>> 
>> Jerry Van Kolken
>> 
>> Millennium Fire Protection Corp. 
>> 
>> 101 Copperwood Way, Suite H
>> 
>> Oceanside, CA 92058
>> 
>> (760) 722-2722 FX 722-2730
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to