It comes from observing there is a 50 deg F difference between the maximum ceiling temperature and the middle of the temperature classification range that is appropriate for the maximum ceiling temperature.
> On Mar 11, 2015, at 12:37 PM, Jerry Van Kolken <[email protected]> wrote: > > Matt, > > Thanks, I didn't consider that. But for conversation sake, let's say that > the style the customer is requesting only comes in ordinary temp (i.e. flat > plate residential concealer) > > Tony / Allen, > > I'm not familiar with the 50 deg rule you guys are referent to, could you > explain. > > Thanks > > Jerry Van Kolken > Millennium Fire Protection > (760) 722-2722 > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Matt Grise > Sent: Wednesday, March 11, 2015 10:02 AM > To: [email protected] > Subject: RE: Spacing to a Radiant Heat Panel > > If the water comes in at 140, and intermediate temperature heads are ok to a > max ceiling temperature of 150 - is there any reason that you could not > just use intermediate temperature heads and then not worry about it? It > seems like the max temperature of the panels would be 140 degrees (F?). > > Matt Grisé PE*, LEED AP, NICET II > Sales Engineer > Alliance Fire Protection > 130 w 9th Ave. > North Kansas City, MO 64116 > > *Licensed in KS & MO > > 913.888.0647 ph > 913.888.0618 f > 913.927.0222 cell > www. AFPsprink.com > > > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Roland Huggins > Sent: Wednesday, March 11, 2015 11:58 AM > To: [email protected] > Subject: Re: Spacing to a Radiant Heat Panel > > The separation from the diffuser is based on heat transfer by convection. > This is a radiation problem. The equation is easy enough but defining the > coefficient is the great unknown. Does FM had any guidance? Wish I had a > better answer for you. > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org <http://www.firesprinkler.org/> > > > > > >> On Mar 10, 2015, at 9:14 PM, Tony Silva <[email protected]> wrote: >> >> I will question the 124 BTU's, assuming it is BTU/hour, which works out to > about 37 watts, which is very small. Could it be BTU/Hr per linear foot > maybe? In the past I have located sprinklers using the requirement for hot > air diffusers. But it would be safer to find out the temperature at the > panel and use a minimum safety of 50 deg.F. >> >> Tony >> >> ----- Original Message ----- >> >> From: "Jerry Van Kolken" <[email protected]> >> To: [email protected] >> Sent: Tuesday, March 10, 2015 5:29:49 PM >> Subject: Spacing to a Radiant Heat Panel >> >> Has anyone dealt with Radiant Heat Panels in the ceiling? >> >> >> >> I have project that will be using these panels with a water >> temperature feed of 140 deg. The panel will be putting out 124 BTUs. >> But I don't know how to translate that information into a safe >> distance or temp for the sprinkler be. >> >> >> >> Any info is appreciated. >> >> >> >> Jerry Van Kolken >> >> Millennium Fire Protection Corp. >> >> 101 Copperwood Way, Suite H >> >> Oceanside, CA 92058 >> >> (760) 722-2722 FX 722-2730 >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl >> er.org >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl >> er.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org