If the water comes in at 140, and intermediate temperature heads are ok to a 
max ceiling temperature of 150  - is there any reason that you could not just 
use intermediate temperature heads and then not worry about it? It seems like 
the max temperature of the panels would be 140 degrees (F?).

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Wednesday, March 11, 2015 11:58 AM
To: [email protected]
Subject: Re: Spacing to a Radiant Heat Panel

The separation from the diffuser is based on heat transfer by convection.  This 
is a radiation problem.  The equation is easy enough but defining the 
coefficient is the great unknown.  Does FM had any guidance?   Wish I had a 
better answer for you.

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Mar 10, 2015, at 9:14 PM, Tony Silva <[email protected]> wrote:
> 
> I will question the 124 BTU's, assuming it is BTU/hour, which works out to 
> about 37 watts, which is very small. Could it be BTU/Hr per linear foot 
> maybe? In the past I have located sprinklers using the requirement for hot 
> air diffusers. But it would be safer to find out the temperature at the panel 
> and use a minimum safety of 50 deg.F. 
> 
> Tony
> 
> ----- Original Message -----
> 
> From: "Jerry Van Kolken" <[email protected]>
> To: [email protected]
> Sent: Tuesday, March 10, 2015 5:29:49 PM
> Subject: Spacing to a Radiant Heat Panel
> 
> Has anyone dealt with Radiant Heat Panels in the ceiling? 
> 
> 
> 
> I have project that will be using these panels with a water 
> temperature feed of 140 deg. The panel will be putting out 124 BTUs. 
> But I don't know how to translate that information into a safe 
> distance or temp for the sprinkler be.
> 
> 
> 
> Any info is appreciated. 
> 
> 
> 
> Jerry Van Kolken
> 
> Millennium Fire Protection Corp. 
> 
> 101 Copperwood Way, Suite H
> 
> Oceanside, CA 92058
> 
> (760) 722-2722 FX 722-2730
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org