Assuming you are in a high rise building...

>From IBC 2013
SECTION 2702 EMERGENCY AND STANDBY POWER SYSTEMS
[F] 2702.2 Where required. 
Emergency and standby power systems shall be provided where required by 
Sections 2702.2.1 through 2702.2.20.

[F] 2702.2.15 High-rise buildings. 
Emergency and standby power shall be provided in high-rise buildings in 
accordance with Sections 403.4.8 and 403.4.9.

SECTION 403 HIGH-RISE BUILDINGS
[F] 403.4 Emergency systems. 
The detection, alarm and emergency systems of high-rise buildings shall comply 
with Sections 403.4.1 through 403.4.9.

[F] 403.4.9 Emergency power systems. 
An emergency power system complying with Chapter 27 shall be provided for 
emergency power loads specified in Section 403.4.9.1.

[F] 403.4.9.1 Emergency power loads. 
The following are classified as emergency power loads:
1. Exit signs and means of egress illumination required by Chapter 10;
2. Elevator car lighting;
3. Emergency voice/alarm communications systems;
4. Automatic fire detection systems;
5. Fire alarm systems; and
6. Electrically powered fire pumps.


Duane Johnson
Strickland Fire Protection


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jay Stough
Sent: Thursday, March 19, 2015 7:54 AM
To: Sprinkler Forum
Subject: Pump transfer Switch

When is a transfer switch required by the IBC or IFC?  We have a customer that 
has a 7 story building with a fire pump (only 50 psi @ 750 with a street static 
of 52).  It has a problem with the controller and parts are no longer 
available.  We gave them a price to change out with a new controller, like for 
like, which includes a transfer switch.  Now they want a price to replace 
without a transfer switch.  I see that NFPA 20 (2007)
10.8.1 says to install a transfer switch if required by the AHJ or 9.3.2.
9.3.2 lays out the requirements for alternate power.  I see that 9.3.1 says an 
alternate power is required when the height of the building is beyond the 
pumping requirements of the fire dept.
  Of course as part of the contract he wants us to get the approvals for 
removing the transfer switch.  I am trying to see what I am up against in 
trying to remove this switch.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to