Jay,  

Is the question when is a transfer switch required or when is alternate
power required ?.  A transfer switch will always be required when there is
more than one source of power, there has to be a method of selecting one
source of power over another.  

Not sure what your adopted codes and standards stipulate, but with regards
to existing buildings one often has to research where the alternate power
source requirement came from in the first place and not necessarily current
code requirements unless of course your jurisdiction has retroactivity
provisions.  Assuming there's not a prescriptive requirement (IBC/IFC/Local
Amendment/Prior Approval) otherwise, one could make a case where a power
source was deemed to be not reliable in the past and improvements made where
the source is now reliable. For example, overhead service conductors that
have been relocated underground.  

In any case here's the NEC language;

NEC 695.1 Scope

(A) Covered. This article covers the installation of the following:
(1) Electric power sources and interconnecting circuits
(2) Switching and control equipment dedicated to fire pump drivers

(B) Not Covered. This article does not cover the following:
(3) Transfer equipment upstream of the fire pump transfer switch(s)

Informational Note: See NFPA 20-2013, Standard for the Installation of
Stationary Pumps for Fire Protection, for further information.

The requirements covering reliable power supplies for electric fire pump
motors correlate with those in NFPA 20, Standard for the Installation of
Stationary Pumps for Fire Protection. However, the NEC and NFPA 20 have a
distinct division of responsibility for fire pump requirements. Performance
issues, including the determination of power supply reliability, are under
the jurisdiction of the NFPA Technical Committee on Fire Pumps, while
electrical installation requirements are within the purview of the National
Electrical Code Committee. The scope of Article 695 speaks to this division
of responsibility. 

695.3 Power Source(s) for Electric Motor-Driven Fire Pumps Electric
motor-driven fire pumps shall have a reliable source of power.

The determination of whether the serving electric utility is a reliable
source of power is an issue for the AHJ. The following excerpt of A.9.3.2 in
Annex A of NFPA 20 elaborates on several key characteristics of a reliable
power supply:

A.9.3.2 A reliable power source possesses the following characteristics:
(1) The source power plant has not experienced any shutdowns longer than 4
continuous hours in the year prior
(2) Power outages have not routinely been experienced in the area of the
protected facility caused by failures in generation or transmission
(3) The normal source of power is not supplied by overhead conductors
outside the protected facility.
(4) Only the disconnect switches and overcurrent protection devices
permitted by 9.2.3 are installed in the normal source of power

Hope this helps,

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jay Stough
Sent: Thursday, March 19, 2015 7:54 AM
To: Sprinkler Forum
Subject: Pump transfer Switch

When is a transfer switch required by the IBC or IFC?  We have a customer
that has a 7 story building with a fire pump (only 50 psi @ 750 with a
street static of 52).  It has a problem with the controller and parts are no
longer available.  We gave them a price to change out with a new controller,
like for like, which includes a transfer switch.  Now they want a price to
replace without a transfer switch.  I see that NFPA 20 (2007)
10.8.1 says to install a transfer switch if required by the AHJ or 9.3.2.
9.3.2 lays out the requirements for alternate power.  I see that 9.3.1 says
an alternate power is required when the height of the building is beyond the
pumping requirements of the fire dept.
  Of course as part of the contract he wants us to get the approvals for
removing the transfer switch.  I am trying to see what I am up against in
trying to remove this switch.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to