Jay, If the existing building was required to have emergency power and therefore an auto-transfer switch for this fire pump, then you must maintain this condition. Unless the occupancy has changed and the building no longer requires it. The AHJ would have to approve a condition like this. You may consider a matching controller and re-use the existing transfer switch. Just a thought.
Lamar Vaughn, SET On Thu, Mar 19, 2015 at 6:53 AM, Jay Stough <[email protected]> wrote: > When is a transfer switch required by the IBC or IFC? We have a customer > that has a 7 story building with a fire pump (only 50 psi @ 750 with a > street static of 52). It has a problem with the controller and parts are > no longer available. We gave them a price to change out with a new > controller, like for like, which includes a transfer switch. Now they want > a price to replace without a transfer switch. I see that NFPA 20 (2007) > 10.8.1 says to install a transfer switch if required by the AHJ or 9.3.2. > 9.3.2 lays out the requirements for alternate power. I see that 9.3.1 says > an alternate power is required when the height of the building is beyond > the pumping requirements of the fire dept. > Of course as part of the contract he wants us to get the approvals for > removing the transfer switch. I am trying to see what I am up against in > trying to remove this switch. > > *Jay Stough* > NICET IV LAYOUT > NICET III ITM > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org