Jay,

If the existing building was required to have emergency power and therefore
an auto-transfer switch for this fire pump, then you must maintain this
condition. Unless the occupancy has changed and the building no longer
requires it. The AHJ would have to approve a condition like this. You may
consider a matching controller and re-use the existing transfer switch.
Just a thought.

Lamar Vaughn, SET

On Thu, Mar 19, 2015 at 6:53 AM, Jay Stough <[email protected]> wrote:

> When is a transfer switch required by the IBC or IFC?  We have a customer
> that has a 7 story building with a fire pump (only 50 psi @ 750 with a
> street static of 52).  It has a problem with the controller and parts are
> no longer available.  We gave them a price to change out with a new
> controller, like for like, which includes a transfer switch.  Now they want
> a price to replace without a transfer switch.  I see that NFPA 20 (2007)
> 10.8.1 says to install a transfer switch if required by the AHJ or 9.3.2.
> 9.3.2 lays out the requirements for alternate power.  I see that 9.3.1 says
> an alternate power is required when the height of the building is beyond
> the pumping requirements of the fire dept.
>   Of course as part of the contract he wants us to get the approvals for
> removing the transfer switch.  I am trying to see what I am up against in
> trying to remove this switch.
>
> *Jay Stough*
> NICET IV LAYOUT
> NICET III ITM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to