I believe there is a clause that says you need it if the FD pumping equipment 
cannot provide the pressure.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jay Stough
Sent: Thursday, March 19, 2015 7:19 AM
To: Sprinkler Forum
Subject: Re: Pump transfer Switch

Since the height of the highest floor of the building is less than 75'
above the fire dept. access, I don't think this classifies as a high rise 
building per IBC (2009 good old Penna) 202 definitions.  So is there anywhere 
else that might require it?

*Jay Stough*
NICET IV LAYOUT
NICET III ITM

On Thu, Mar 19, 2015 at 8:04 AM, Duane Johnson <[email protected]>
wrote:

> Assuming you are in a high rise building...
>
> From IBC 2013
> SECTION 2702 EMERGENCY AND STANDBY POWER SYSTEMS [F] 2702.2 Where 
> required.
> Emergency and standby power systems shall be provided where required 
> by Sections 2702.2.1 through 2702.2.20.
>
> [F] 2702.2.15 High-rise buildings.
> Emergency and standby power shall be provided in high-rise buildings 
> in accordance with Sections 403.4.8 and 403.4.9.
>
> SECTION 403 HIGH-RISE BUILDINGS
> [F] 403.4 Emergency systems.
> The detection, alarm and emergency systems of high-rise buildings 
> shall comply with Sections 403.4.1 through 403.4.9.
>
> [F] 403.4.9 Emergency power systems.
> An emergency power system complying with Chapter 27 shall be provided 
> for emergency power loads specified in Section 403.4.9.1.
>
> [F] 403.4.9.1 Emergency power loads.
> The following are classified as emergency power loads:
> 1. Exit signs and means of egress illumination required by Chapter 10; 
> 2. Elevator car lighting; 3. Emergency voice/alarm communications 
> systems; 4. Automatic fire detection systems; 5. Fire alarm systems; 
> and 6. Electrically powered fire pumps.
>
>
> Duane Johnson
> Strickland Fire Protection
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Jay 
> Stough
> Sent: Thursday, March 19, 2015 7:54 AM
> To: Sprinkler Forum
> Subject: Pump transfer Switch
>
> When is a transfer switch required by the IBC or IFC?  We have a 
> customer that has a 7 story building with a fire pump (only 50 psi @ 
> 750 with a street static of 52).  It has a problem with the controller 
> and parts are no longer available.  We gave them a price to change out 
> with a new controller, like for like, which includes a transfer 
> switch.  Now they want a price to replace without a transfer switch.  
> I see that NFPA 20 (2007)
> 10.8.1 says to install a transfer switch if required by the AHJ or 9.3.2.
> 9.3.2 lays out the requirements for alternate power.  I see that 9.3.1 
> says an alternate power is required when the height of the building is 
> beyond the pumping requirements of the fire dept.
>   Of course as part of the contract he wants us to get the approvals 
> for removing the transfer switch.  I am trying to see what I am up 
> against in trying to remove this switch.
>
> *Jay Stough*
> NICET IV LAYOUT
> NICET III ITM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to