Hello Jay,

NFPA 20 2013 9.3 list conditions.  

Thursday, March 19, 2015, 8:19:23 AM, you wrote:

> Since the height of the highest floor of the building is less than 75'
> above the fire dept. access, I don't think this classifies as a high rise
> building per IBC (2009 good old Penna) 202 definitions.  So is there
> anywhere else that might require it?

> *Jay Stough*
> NICET IV LAYOUT
> NICET III ITM

> On Thu, Mar 19, 2015 at 8:04 AM, Duane Johnson <[email protected]>
> wrote:

>> Assuming you are in a high rise building...

>> From IBC 2013
>> SECTION 2702 EMERGENCY AND STANDBY POWER SYSTEMS
>> [F] 2702.2 Where required.
>> Emergency and standby power systems shall be provided where required by
>> Sections 2702.2.1 through 2702.2.20.

>> [F] 2702.2.15 High-rise buildings.
>> Emergency and standby power shall be provided in high-rise buildings in
>> accordance with Sections 403.4.8 and 403.4.9.

>> SECTION 403 HIGH-RISE BUILDINGS
>> [F] 403.4 Emergency systems.
>> The detection, alarm and emergency systems of high-rise buildings shall
>> comply with Sections 403.4.1 through 403.4.9.

>> [F] 403.4.9 Emergency power systems.
>> An emergency power system complying with Chapter 27 shall be provided for
>> emergency power loads specified in Section 403.4.9.1.

>> [F] 403.4.9.1 Emergency power loads.
>> The following are classified as emergency power loads:
>> 1. Exit signs and means of egress illumination required by Chapter 10;
>> 2. Elevator car lighting;
>> 3. Emergency voice/alarm communications systems;
>> 4. Automatic fire detection systems;
>> 5. Fire alarm systems; and
>> 6. Electrically powered fire pumps.


>> Duane Johnson
>> Strickland Fire Protection


>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Jay Stough
>> Sent: Thursday, March 19, 2015 7:54 AM
>> To: Sprinkler Forum
>> Subject: Pump transfer Switch

>> When is a transfer switch required by the IBC or IFC?  We have a customer
>> that has a 7 story building with a fire pump (only 50 psi @ 750 with a
>> street static of 52).  It has a problem with the controller and parts are
>> no longer available.  We gave them a price to change out with a new
>> controller, like for like, which includes a transfer switch.  Now they want
>> a price to replace without a transfer switch.  I see that NFPA 20 (2007)
>> 10.8.1 says to install a transfer switch if required by the AHJ or 9.3.2.
>> 9.3.2 lays out the requirements for alternate power.  I see that 9.3.1
>> says an alternate power is required when the height of the building is
>> beyond the pumping requirements of the fire dept.
>>   Of course as part of the contract he wants us to get the approvals for
>> removing the transfer switch.  I am trying to see what I am up against in
>> trying to remove this switch.

>> *Jay Stough*
>> NICET IV LAYOUT
>> NICET III ITM
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]

>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]

>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-- 
Best regards,
 Charles                            mailto:[email protected]