But I am right in thinking this system, if designed to the NFPA-13 standard,
should be limited to 40,000 sq. ft?

John Paulsen
Crown Fire System Design, LLC
6282 Seeds Road
Grove City, OH 43123
P – 614-782-2438
F – 614-782-2374
C – 614-348-8206
Email – [email protected]

 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Matt Grise
Sent: Wednesday, November 11, 2015 2:17 PM
To: [email protected]
Subject: RE: General Storage

It could have originally incorporated some light or ordinary hazard space in
addition to the extra. It could also have been set up using FM system size
limits (60ksf).

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of CAD Station
Sent: Wednesday, November 11, 2015 1:15 PM
To: [email protected]
Subject: General Storage

AFSA Forums:

 

I want to clear up a question that has been bothering me since looking at
plans for an addition to an existing warehouse. The project is a plastic
manufacturing and warehousing facility of non-combustible steel bar joist
construction. The storage height is limited to 8' max. The design layout is
CMSA VK580, 16.8K sprinklers spaced at 100 sq. ft . The design density is
.45 / 2500 sq. ft. 

 

My question is this; according to figure 11.2.3.1.1 this is a Ex Haz Grp II
density and by my interpretation, the overhead system should be limited to
40,000 sq. ft. total area. However, the existing system that was done by
another contractor covers 50,000 sq ft. Have I been looking at this wrong
all these years since 231-C was incorporated into NFPA-13? Is storage of PVC
plastic commodities to 8' an Ord Haz Grp II occupancy?

 

Thanks, 

 

John Paulsen

Crown Fire System Design, LLC

6282 Seeds Road

Grove City, OH 43123

P - 614-782-2438

F - 614-782-2374

C - 614-348-8206

Email -  <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to