Larry / Roland:

Thank you very much for your help. Your inputs are greatly appreciated.
While the end result for the system coverage area remains the same, the
original question highlights the danger that we all face in trying to make
critical design decisions with incomplete or erroneous information regarding
the proposed protected hazard. While I have been at this for quite a while,
being a one man band, I miss having the ability to collaborate with
co-workers on issues just like this. I heartily applaud AFSA for creating
this forum and look forward to participating in the future. 

Thanks Again,

John Paulsen
Crown Fire System Design, LLC
6282 Seeds Road
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206
Email - [email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Wednesday, November 11, 2015 6:59 PM
To: [email protected]
Subject: Re: General Storage

A perfect example on getting an accurate assignment on the commodity as a
first step.  Hard to argue with Larry on this stuff but after sitting on
NFPA 13 with him for 20 years. one has to try occasionally.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Nov 11, 2015, at 2:42 PM, Larry Keeping <[email protected]> wrote:
> 
> I've been watching this thread and though that I'd put my oar in.
> 
> The message that started the conversation referenced storage of PVC to a
height of 8 ft. As per the examples in Table A.5.6.3 and Table A.5.6.3.3,
PVC can be considered a Class III commoditiy (There might be an exception if
it is highly plasticized, there used to be but I can't find it today).
However, with the Class III designation to less than 12 ft storage it could
be protected per Table 13.2.1 via the OH2 curve  of Figure 13.2.1.
> 
> The 40000 sq ft system size requirement is for Section 8.2.1(3) extra
hazard and for Section 8.2.1(4) high piled storage, so it wouldn't apply to
this scenario. (In the new 2016 edition that would be identified as "low
piled storage".)
> 
> Section 13.2.2 permits installation by NFPA 13 and design criteria and
modifiers as ... Chapter 11 for ordinary hazard ...
> So that  should throw you back to Section 8.2.1(2). Therefore a system
size of 52000 sq ft would be acceptable, even if the whole facility was used
for that storage configuration.
> 
> Larry Keeping

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to