Per NFPA 13, system size is limited to 52k sq ft.  Of that, only 40k sq ft
can be storage/EH areas.  So, if there were 10k sq ft of non-storage space
and 40k sq ft of storage space, then it would be correct.  If there is only
storage/EH areas, then system size is obviously limited to 40k sq ft.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 11/11/2015 1:55 PM, CAD Station wrote:
> But I am right in thinking this system, if designed to the NFPA-13 
> standard, should be limited to 40,000 sq. ft?
>
> John Paulsen
> Crown Fire System Design, LLC
> 6282 Seeds Road
> Grove City, OH 43123
> P – 614-782-2438
> F – 614-782-2374
> C – 614-348-8206
> Email – [email protected]
>
>   
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]]
> On Behalf Of Matt Grise
> Sent: Wednesday, November 11, 2015 2:17 PM
> To: [email protected]
> Subject: RE: General Storage
>
> It could have originally incorporated some light or ordinary hazard 
> space in addition to the extra. It could also have been set up using 
> FM system size limits (60ksf).
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>   
> 913.888.0647 ph
> 913.888.0618 f
> 913.526.7443 cell
> www. AFPsprink.com
>   
>
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]]
> On Behalf Of CAD Station
> Sent: Wednesday, November 11, 2015 1:15 PM
> To: [email protected]
> Subject: General Storage
>
> AFSA Forums:
>
>   
>
> I want to clear up a question that has been bothering me since looking 
> at plans for an addition to an existing warehouse. The project is a 
> plastic manufacturing and warehousing facility of non-combustible 
> steel bar joist construction. The storage height is limited to 8' max. 
> The design layout is CMSA VK580, 16.8K sprinklers spaced at 100 sq. ft 
> . The design density is
> .45 / 2500 sq. ft.
>
>   
>
> My question is this; according to figure 11.2.3.1.1 this is a Ex Haz 
> Grp II density and by my interpretation, the overhead system should be 
> limited to
> 40,000 sq. ft. total area. However, the existing system that was done 
> by another contractor covers 50,000 sq ft. Have I been looking at this 
> wrong all these years since 231-C was incorporated into NFPA-13? Is 
> storage of PVC plastic commodities to 8' an Ord Haz Grp II occupancy?
>
>   
>
> Thanks,
>
>   
>
> John Paulsen
>
> Crown Fire System Design, LLC
>
> 6282 Seeds Road
>
> Grove City, OH 43123
>
> P - 614-782-2438
>
> F - 614-782-2374
>
> C - 614-348-8206
>
> Email -  <mailto:[email protected]> [email protected]
>
>   
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to