You didn't ask for a second opinion, but I would just like to add that this is 
actually one of the more obvious no-brainer questions that might be posed in 
the layout of a sprinkler system. I'm not sure that its well enough known that 
CPVC is listed for underground use. I have wrestled with AHJs who first 
rejected the proposed application and then insisted that it had to be dressed 
blocked after we got over that first hump. But NFPA 13 and 24 as well as the 
manufacturers' installation guidelines make it clear that this product can be 
very easily and universally applied to underground applications and as a fusion 
joint does not require any extreme methods for thrust restraint.

We use it to cross walkways and connect accessory structures to larger building 
systems all the time. We've done it in both public and private projects and its 
not only easier and cheaper to install than any metallic piping, it's likely to 
be infinitely longer lived.


Steve


-------- Original message --------
From: Brian Harris <[email protected]>
Date: 1/8/2016 6:22 AM (GMT-08:00)
To: [email protected]
Subject: RE: Galvanized Pipe

Mark-
Thanks for the info. It was actually the GC that recommended we use galvanized 
pipe "because that's how they always have done it"...... CPVC it is.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, January 08, 2016 9:14 AM
To: [email protected]
Subject: Re: Galvanized Pipe

In my experience galvanized pipe used underground is a great method if you're a 
service company that makes a living doing repair and maintenance on fire 
sprinkler systems. But if you're interested in maintaining a good customer 
relationship, it is possibly the worst choice. Cpvc is listed for underground 
service and is a much better long term option for this application.

Mark at Aero
602 820-7894

Sent from my iPhone

> On Jan 8, 2016, at 6:49 AM, "Brian Harris" <[email protected]> wrote:
>
> Has anybody ever used galvanized pipe to go underground (slab) to get from 
> one side of an apartment breezeway to the other ?
>
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to