Cecil
If the job is NFPA 13R, NFPA 24 does not apply (See the scope below from NFPA 
24)
Your friend
Pete

1.1.4 This standard shall not apply to underground mains
serving sprinkler systems designed and installed in accordance
with NFPA 13R that are less than 4 in. (100 mm) in nominal
diameter.


Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Sprinkler Academy - C Bilbo
Sent: Friday, January 08, 2016 10:39 AM
To: [email protected]
Subject: RE: Galvanized Pipe

Brian,
 
To further what my two friends have already said, not only is this a bad idea, 
it is not permitted.  Chapter 10 in NFPA 13 only allows the use of galvanized 
steel as underground pipe when it feeds a fire department connection.  When 
this section is applied it must also be wrapped and coated.  The method for 
wrapping and coating must be approved.
 
When the justification for doing something incorrectly is, "Because that's the 
way we have always done it..." I think to myself, 'they just admitted to always 
doing the wrong thing'.  Then, I sit down with them and have a cordial 
conversation about the best way to move forward.

It should be recognized that the above is my opinion as a member of the NFPA 13 
Committee, and has not been processed as a formal interpretation in accordance 
with the NFPA Regulations Governing Committee Projects and should therefore not 
be considered, nor relied upon, as the official position of the the NFPA, nor 
any of their technical committees. 

Sincerely,


Cecil Bilbo 
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com

[email protected]

 

OUR STUDENTS SAVE LIVES!!


 
> From: [email protected]
> To: [email protected]
> Subject: Galvanized Pipe
> Date: Fri, 8 Jan 2016 13:49:43 +0000
> 
> Has anybody ever used galvanized pipe to go underground (slab) to get from 
> one side of an apartment breezeway to the other ?
> 
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to