Scott,

Isn't 36.10M for Welded and Seamless pipe?
B16.4  is for fittings.

R/
Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
*NEW ADDRESS*
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, January 18, 2016 7:27 AM
To: [email protected]
Subject: RE: Ductile Iron Fittings

Thanks for all the responses. 

The reason is because NFPA 13 does not include ductile iron (ASME B36.10M) in 
the acceptable materials table. My opinion is that it is functionally more than 
adequate. 

Would this be covered by section 1.7 (2016) for alternate arrangements?

    J. Scott Mitchell, PE
       Fire Protection Engineer | 
       Projects Engineering
       CNS Pantex | 806.477.5883 | 