B16.4 is for gray iron which I think is the most common form for fire sprinkler
system above ground threaded fittings.
I'm attempting to determine the applicable standard for ductile iron flanged
fittings AND whether or not such fittings are permissible in the above ground
portion of the fire sprinkler system. Specifically in the riser manifold. It
could be a flanged ductile iron tee or flanged ductile iron spool piece, etc.
I heard that they are being used as I described. So, I thought I'd look it up
to see if NFPA 13 allowed it. And, none of the standards listed in the
acceptable materials table address ductile iron.
I'm comfortable with pointing to 1.7 as a "back up" justification. But, any
more help would be appreciated.
J. Scott Mitchell, PE
Fire Protection Engineer |
Projects Engineering
CNS Pantex | 806.477.5883 |
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Matthew J Willis
Sent: Monday, January 18, 2016 2:29 PM
To: [email protected]
Subject: RE: Ductile Iron Fittings
Scott,
Isn't 36.10M for Welded and Seamless pipe?
B16.4 is for fittings.
R/
Matt
Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
*NEW ADDRESS*
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of [email protected]
Sent: Monday, January 18, 2016 7:27 AM
To: [email protected]
Subject: RE: Ductile Iron Fittings
Thanks for all the responses.
The reason is because NFPA 13 does not include ductile iron (ASME B36.10M) in
the acceptable materials table. My opinion is that it is functionally more than
adequate.
Would this be covered by section 1.7 (2016) for alternate arrangements?
J. Scott Mitchell, PE
Fire Protection Engineer |
Projects Engineering
CNS Pantex | 806.477.5883 |
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________