Not a problem.  Fire Flow per the IFC is one area of fire protection 
engineering way too often overlooked, misunderstood or just plain ignored.

Let me know if you have any other questions.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Thursday, May 19, 2016 9:23 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Fire Flow

Craig-
Thanks for the info.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>
Sent: Thursday, May 19, 2016 9:00 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Fire Flow

You need to contact the local fire code authority and find out from them what 
their approved method is for determining Fire Flow.  There are more than a half 
dozen methods that are used.

Once you find the method to be used, you will use the calculation methodology 
prescribed within.

Of the different methods, the results can vary dramatically.

Call the AHJ.

If they say they don't know and don't' care, Appendix B of the IFC is the 
simplest method.  But other methods may be more favorable from a water supply 
standpoint depending on the type of facility you have.

Some don't care if the facility is sprinklered or not, others allow a reduction 
in fire flow if the bldg. is sprinklered.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Thursday, May 19, 2016 8:56 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Fire Flow

Does anybody have a spreadsheet or pdf they'd care to share that is used to 
calculate fire flow demand for a project site & determine underground/tap sizes?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to