Agreed.  By cumulative, I meant the largest single building demand and whatever 
additional flow is needed for adjacent hydrants.  In refinery settings, this is 
all appurtenances and systems that are expected to be used during the single, 
most demanding fire event which likely exceeds a single building.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
[email protected]  \  burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
*Registered in: MN, PA, & TX
**NICET IV - Water-Based Systems Layout

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Thursday, May 19, 2016 10:23 AM
To: [email protected]
Subject: RE: Fire Flow

Right but your comment could be misread as to mean that fire flow for a multi 
building campus is based on multiple buildings. To be clear, fire flow 
requirements are based on the largest (or most demanding by construction type 
if not the largest) building on a site when there is more than one. It is not 
cumulative.


Steve


-------- Original message --------
From: "Hinson, Ryan" <[email protected]<mailto:[email protected]>>
Date: 5/19/16 7:30 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Flow

Your building sprinkler feed is just that...a sprinkler feed which should be 
hydraulically calculated if minimum sizing is desired.  Otherwise, A fire flow 
does not ONLY come through this line, it cumulative in the vicinity.  Fire 
flows are for overall requirements of all adjacent hydrants off the looped main 
which serves both your building as well as others in the proximity.  Fire flow 
must always meet (but will normally exceed) a single building's sprinkler 
demand IMO.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
*Registered in: MN, PA, & TX
**NICET IV - Water-Based Systems Layout

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, May 19, 2016 9:21 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Flow

Steve-
Thanks for the help, I think I got it from here.....

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Thursday, May 19, 2016 10:02 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Flow

It's like sprinkler hydraulics in that the size of the piping may have to be 
calculated, which is based on the available flow and pressure from whatever 
water supply you're starting with. Usually, and I emphasize usually but not 
always, a 6-inch lateral is adequate for a single hydrant but not if its 450 
feet long.


Steve


-------- Original message --------
From: Brian Harris <[email protected]<mailto:[email protected]>>
Date: 5/19/16 6:48 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Flow

Got it, thanks. I see where this particular project requires 1500 gpm @ 20 psi 
for 2 hours, what is needed to translate that into required underground/tap 
size?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>
Sent: Thursday, May 19, 2016 9:44 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Fire Flow

In the IFC it is table B 105.2 i believe.

Mark at Aero
602 820-7894

Sent from my iPad

On May 19, 2016, at 5:56 AM, Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Does anybody have a spreadsheet or pdf they'd care to share that is used to 
calculate fire flow demand for a project site & determine underground/tap sizes?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to