We've scene at least two projects killed because the AHJ refused to grant a 
reduction from the fire code tables. One of those was because of a standing 
policy against traduction in fire flow universally and the other hinged on 13R 
systems.  In that case, the developer had received such bad advice that they 
were under the very sincerely held impression that the cost of 13 systems would 
make their crappy little apartments too expensive to build


Steve


-------- Original message --------
From: Travis Mack <[email protected]>
Date: 5/19/16 6:33 AM (GMT-08:00)
To: [email protected]
Subject: Re: Fire Flow

So true. And I love when the specifying engineers don't research the local 
amendments.

One large jurisdiction here does not allow a reduction in site fire flow for 
13R systems, and only a 50% reduction for 13 systems.

I'm the bad guy when we have to tell the developer that they have potential 
problems because of local requirements.

It's getting better but still happens.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On May 19, 2016, at 6:27 AM, 
<[email protected]<mailto:[email protected]>> 
<[email protected]<mailto:[email protected]>> wrote:

Not a problem.  Fire Flow per the IFC is one area of fire protection 
engineering way too often overlooked, misunderstood or just plain ignored.

Let me know if you have any other questions.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, May 19, 2016 9:23 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Flow

Craig-
Thanks for the info.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>
Sent: Thursday, May 19, 2016 9:00 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Flow

You need to contact the local fire code authority and find out from them what 
their approved method is for determining Fire Flow.  There are more than a half 
dozen methods that are used.

Once you find the method to be used, you will use the calculation methodology 
prescribed within.

Of the different methods, the results can vary dramatically.

Call the AHJ.

If they say they don't know and don't' care, Appendix B of the IFC is the 
simplest method.  But other methods may be more favorable from a water supply 
standpoint depending on the type of facility you have.

Some don't care if the facility is sprinklered or not, others allow a reduction 
in fire flow if the bldg. is sprinklered.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, May 19, 2016 8:56 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Fire Flow

Does anybody have a spreadsheet or pdf they'd care to share that is used to 
calculate fire flow demand for a project site & determine underground/tap sizes?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to