It's like sprinkler hydraulics in that the size of the piping may have to be 
calculated, which is based on the available flow and pressure from whatever 
water supply you're starting with. Usually, and I emphasize usually but not 
always, a 6-inch lateral is adequate for a single hydrant but not if its 450 
feet long.


Steve


-------- Original message --------
From: Brian Harris <[email protected]>
Date: 5/19/16 6:48 AM (GMT-08:00)
To: [email protected]
Subject: RE: Fire Flow

Got it, thanks. I see where this particular project requires 1500 gpm @ 20 psi 
for 2 hours, what is needed to translate that into required underground/tap 
size?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, May 19, 2016 9:44 AM
To: [email protected]
Subject: Re: Fire Flow

In the IFC it is table B 105.2 i believe.

Mark at Aero
602 820-7894

Sent from my iPad

On May 19, 2016, at 5:56 AM, Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Does anybody have a spreadsheet or pdf they'd care to share that is used to 
calculate fire flow demand for a project site & determine underground/tap sizes?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to