I’m not sure what’s to disagree with.   If you see a static pressure on the 
gauge (it could be during a visual and not just a main drain test) that’s near 
or lower than the BOR residual demand on the calc’ card, then you potentially 
have a problem.   This is just comparative metrics:  the question was (if I’m 
recalling and paraphrasing correctly), where do we (composite Forum) locate the 
BOR node for purposes of recording the information on the calc’ card?    And I 
said at the riser gauge for the reasons I’ve mentioned.  I’m haven’t 
recommended any measure of “testing” or any other steps beyond what’s already 
prescribed in NFPA 25.

In our little incident, the owner bit the bullet and paid for it because the 
fire department stepped up and acknowledged that they had furnished the 
information based on the address side and not the connection side of the 
building.   If they hadn’t  … who knows?

SL



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Monday, July 11, 2016 5:30 AM
To: [email protected]
Subject: Re: Base of riser on placards

Steve,
I have to respectfully disagree with you on this.  My main concern would be the 
fact that the drain and gauge are so close together.  On a riser manifold, the 
gauge is usually directly across or slightly above the drain location.  That 
would be equivalent to taking the residual pressure from a flowing hydrant, 
wouldn't it?
In addition, as my original post alluded to, if your BOR node is on the suction 
side of the backflow preventer, the lower flow from the drain or inspectors 
test will create a higher friction loss from the backflow than was accounted 
for during the hydraulic calculations (normally, I'm sure not all BFPs have 
that larger pressure loss at lower flows, but most I've seen do,).

Just out of curiosity as well, how long was the installing sprinkler contractor 
blamed for that issue you had?
I guess my point is, we already have acceptance testing in NFPA 13, as well as 
hydraulic calculation procedures, licensing (in most states) etc.
Using the main drain test for anything other than an NFPA 25 inspection point 
is slippery slope that I don't think we should be going down.
Thanks,
Ben


Benjamin Young

On Fri, Jul 8, 2016 at 1:43 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
I’ve always looked at it as a red-flag benchmark.   The residual demand at BOR 
takes static lift and friction loss to the remote area into account, so if I do 
a main drain test and I look at the calc’ card and read that the demand is … 
whatever, 63.5 PSI @ 331.7 GPM.   And then I look at the gauge and it says 89 
PSI static.  And then I open the main drain and residual drops to 81 PSI … 
great.  But if I open that drain and it drops to 60 PSI or if look at static 
and it says 68 PSI and then drops to 60 … then something is amiss.    I have 
actually seen commissioning testing where the main drain flow test on final 
inspection called attention to the fact that the flow test was taken on a 
different main than the one feeding the system.   And it turned out that the 
one feeding the system was separated from the rest of the public system zone by 
a pressure regulating station.   And that the entire system was not 
hydraulically capable of meeting its demand.

Extreme example to be sure but if you have even a passing understanding of 
hydraulics, comparing the main drain test results to the BOR demand is a 
substantive metric.

SL

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of rongreenman .
Sent: Friday, July 08, 2016 10:29 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Base of riser on placards

So I have the total demand at the BOR and the expected pressure loss from 
static with the entire design area flowing. How does a main drain test simulate 
this? My understanding of the main drain test is a comparative analysis of 
pressure drop as recorded at acceptance from the Contractor's Above Ground 
Materials and Test Certificate with the pressure drop at the time of the test. 
I presume that original data is what is noted under the area of the placard for 
"Supply Data" and is irrelevant regarding the calculations.



On Fri, Jul 8, 2016 at 10:16 AM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
The information of value at least once a year when you do the main drain test.  
 Maybe you could add both BOR and Source demands, but I don’t agree with 
posting Source data in lieu of BOR.

SL

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Todd Williams
Sent: Friday, July 08, 2016 10:15 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Base of riser on placards

I'll ask the unthinkable question, is the BoR demand on the placard worthwhile? 
Hydraulic calculations are done back to the effective point of the flow test. 
The underground losses, hose demand and sometimes backflow preventer losses are 
taken before the BoR. Consequently you cannot compare the BoR demand to a new 
public water test and make a valid conclusion without a full set of original 
plans and calculations. Wouldn't it make more sense to put the demand at the 
water source on the placard?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-608-4559<tel:860-608-4559> (cell)

Sent using CloudMagic<https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>

On Fri, Jul 8, 2016 at 10:21 AM, Ed Kramer 
<[email protected]<mailto:[email protected]>> wrote:
I’ve asked this question in the past and the answers have been all over the 
board.

I tend to think the BOR location needs to be consistent from project to 
project, whether it’s a single system riser or multiple system risers. In our 
part of the universe, most (but not all) backflow preventers are located inside 
the building immediately downstream of the underground flange. I locate the BOR 
at the underground flange on all systems. By placing data from that location on 
the Hydraulic Design Placard, it makes it easier for someone else to compare 
the sprinkler system demand to water supply data.

I believe the intent is to include the combined hose allowance, but got nothing 
from the standard to back that up. With a strong water supply (lots of volume), 
available pressure while flowing the sprinkler plus hose demand is going to be 
virtually the same as pressure available while flowing only sprinkler demand. 
But many of the water supplies we work with are marginal. Removing 100, 250 or 
500 gpm combined hose allowance from the water supply can make a very 
significant difference in available pressure. So when comparing sprinkler 
demand to water supply data, knowing the combined hose allowance is very 
helpful.

Respectfully,
Ed Kramer
Bamford Fire Sprinkler



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Thursday, July 07, 2016 3:06 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Base of riser on placards

What's the general consensus on the location of the 'base of riser' for 
hydraulic placards that everyone uses? See Figure A 24.5 in the 2010 Edition of 
13 and/or 24.5.2
I feel its supposed to be at the base of each sprinkler riser (where you have 
multiple systems) where it ties into a common header.
Others in my office think its where the incoming flange comes into the riser 
room.
If you have a vertical riser with a vertical backflow, then these two points 
would be the same with either method in my line of thinking.
Also, is the hose indicated on the placards supposed to be inside hose only, or 
combined in and out?  I just realized after reading this today that it could 
only be referring to inside hose, but I've always put the combined hose there...
Thanks,

Benjamin Young

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]<mailto:[email protected]>

253.576.9700<tel:253.576.9700>

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958)

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to