Steve,

I wasn't clear, sorry.  I was referring specifically and only to the
residual pressure reading during a drain test.  I could see how that could
be confusing.  Yes, the static pressure would be a definite red flag if its
lower than the residual.

You mentioned commissioning in your original post, so I assumed you were
dealing with a new installation as well, not an existing one that would
fall under 25.  When I originally wrote this last week I was coming from
that frame of reference (a new installation that's getting acceptance
tested).

I think that explains the confusion, sorry about that.

-Ben


Benjamin Young

On Mon, Jul 11, 2016 at 11:14 AM, Steve Leyton <[email protected]>
wrote:

> I’m not sure what’s to disagree with.   If you see a static pressure on
> the gauge (it could be during a visual and not just a main drain test)
> that’s near or lower than the BOR residual demand on the calc’ card, then
> you potentially have a problem.   This is just comparative metrics:  the
> question was (if I’m recalling and paraphrasing correctly), where do we
> (composite Forum) locate the BOR node for purposes of recording the
> information on the calc’ card?    And I said at the riser gauge for the
> reasons I’ve mentioned.  I’m haven’t recommended any measure of “testing”
> or any other steps beyond what’s already prescribed in NFPA 25.
>
>
>
> In our little incident, the owner bit the bullet and paid for it because
> the fire department stepped up and acknowledged that they had furnished the
> information based on the address side and not the connection side of the
> building.   If they hadn’t  … who knows?
>
>
> SL
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Ben Young
> *Sent:* Monday, July 11, 2016 5:30 AM
>
> *To:* [email protected]
> *Subject:* Re: Base of riser on placards
>
>
>
> Steve,
>
> I have to respectfully disagree with you on this.  My main concern would
> be the fact that the drain and gauge are so close together.  On a riser
> manifold, the gauge is usually directly across or slightly above the drain
> location.  That would be equivalent to taking the residual pressure from a
> flowing hydrant, wouldn't it?
>
> In addition, as my original post alluded to, if your BOR node is on the
> suction side of the backflow preventer, the lower flow from the drain or
> inspectors test will create a higher friction loss from the backflow than
> was accounted for during the hydraulic calculations (normally, I'm sure not
> all BFPs have that larger pressure loss at lower flows, but most I've seen
> do,).
>
> Just out of curiosity as well, how long was the installing sprinkler
> contractor blamed for that issue you had?
>
> I guess my point is, we already have acceptance testing in NFPA 13, as
> well as hydraulic calculation procedures, licensing (in most states) etc.
>
> Using the main drain test for anything other than an NFPA 25 inspection
> point is slippery slope that I don't think we should be going down.
>
> Thanks,
>
> Ben
>
>
>
> Benjamin Young
>
>
>
> On Fri, Jul 8, 2016 at 1:43 PM, Steve Leyton <[email protected]>
> wrote:
>
> I’ve always looked at it as a red-flag benchmark.   The residual demand at
> BOR takes static lift and friction loss to the remote area into account, so
> if I do a main drain test and I look at the calc’ card and read that the
> demand is … whatever, 63.5 PSI @ 331.7 GPM.   And then I look at the gauge
> and it says 89 PSI static.  And then I open the main drain and residual
> drops to 81 PSI … great.  But if I open that drain and it drops to 60 PSI
> or if look at static and it says 68 PSI and then drops to 60 … then
> something is amiss.    I have actually seen commissioning testing where the
> main drain flow test on final inspection called attention to the fact that
> the flow test was taken on a different main than the one feeding the
> system.   And it turned out that the one feeding the system was separated
> from the rest of the public system zone by a pressure regulating station.
> And that the entire system was not hydraulically capable of meeting its
> demand.
>
>
>
> Extreme example to be sure but if you have even a passing understanding of
> hydraulics, comparing the main drain test results to the BOR demand is a
> substantive metric.
>
>
>
> SL
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *rongreenman
> .
> *Sent:* Friday, July 08, 2016 10:29 AM
> *To:* [email protected]
> *Subject:* Re: Base of riser on placards
>
>
>
> So I have the total demand at the BOR and the expected pressure loss from
> static with the entire design area flowing. How does a main drain test
> simulate this? My understanding of the main drain test is a comparative
> analysis of pressure drop as recorded at acceptance from the Contractor's
> Above Ground Materials and Test Certificate with the pressure drop at the
> time of the test. I presume that original data is what is noted under the
> area of the placard for "Supply Data" and is irrelevant regarding the
> calculations.
>
>
>
>
>
>
>
> On Fri, Jul 8, 2016 at 10:16 AM, Steve Leyton <[email protected]>
> wrote:
>
> The information of value at least once a year when you do the main drain
> test.   Maybe you could add both BOR and Source demands, but I don’t agree
> with posting Source data in lieu of BOR.
>
>
>
> SL
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Todd
> Williams
> *Sent:* Friday, July 08, 2016 10:15 AM
> *To:* [email protected]
> *Subject:* RE: Base of riser on placards
>
>
>
> I'll ask the unthinkable question, is the BoR demand on the placard
> worthwhile? Hydraulic calculations are done back to the effective point of
> the flow test. The underground losses, hose demand and sometimes backflow
> preventer losses are taken before the BoR. Consequently you cannot compare
> the BoR demand to a new public water test and make a valid conclusion
> without a full set of original plans and calculations. Wouldn't it make
> more sense to put the demand at the water source on the placard?
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-608-4559 (cell)
>
>
>
> Sent using CloudMagic
> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>
>
>
>
> On Fri, Jul 8, 2016 at 10:21 AM, Ed Kramer <[email protected]> wrote:
>
> I’ve asked this question in the past and the answers have been all over
> the board.
>
>
>
> I tend to think the BOR location needs to be consistent from project to
> project, whether it’s a single system riser or multiple system risers. In
> our part of the universe, most (but not all) backflow preventers are
> located inside the building immediately downstream of the underground
> flange. I locate the BOR at the underground flange on all systems. By
> placing data from that location on the Hydraulic Design Placard, it makes
> it easier for someone else to compare the sprinkler system demand to water
> supply data.
>
>
>
> I believe the intent is to include the combined hose allowance, but got
> nothing from the standard to back that up. With a strong water supply (lots
> of volume), available pressure while flowing the sprinkler plus hose demand
> is going to be virtually the same as pressure available while flowing only
> sprinkler demand. But many of the water supplies we work with are marginal.
> Removing 100, 250 or 500 gpm combined hose allowance from the water supply
> can make a very significant difference in available pressure. So when
> comparing sprinkler demand to water supply data, knowing the combined hose
> allowance is very helpful.
>
>
>
> Respectfully,
>
> Ed Kramer
>
> Bamford Fire Sprinkler
>
>
>
>
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Ben Young
> *Sent:* Thursday, July 07, 2016 3:06 PM
> *To:* [email protected]
> *Subject:* Base of riser on placards
>
>
>
> What's the general consensus on the location of the 'base of riser' for
> hydraulic placards that everyone uses? See Figure A 24.5 in the 2010
> Edition of 13 and/or 24.5.2
>
> I feel its supposed to be at the base of each sprinkler riser (where you
> have multiple systems) where it ties into a common header.
>
> Others in my office think its where the incoming flange comes into the
> riser room.
>
> If you have a vertical riser with a vertical backflow, then these two
> points would be the same with either method in my line of thinking.
>
> Also, is the hose indicated on the placards supposed to be inside hose
> only, or combined in and out?  I just realized after reading this today
> that it could only be referring to inside hose, but I've always put the
> combined hose there...
>
> Thanks,
>
>
> Benjamin Young
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
>
> --
>
> Ron Greenman
>
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> [email protected]
>
> 253.576.9700
>
>
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to