FM has different design categories (HC-1, HC-2, etc). Min hose is 250. No design area reductions. Their Data Sheets are on line but always best to talk to a rep

via Newton Mail [https://cloudmagic.com/k/d/mailapp?ct=pi&cv=9.1.9&pv=10.0.1&source=email_footer_2] On Thu, Sep 29, 2016 at 7:13 AM, Dewayne Martinez <dmarti...@total-mechanical.com> wrote: We are doing a small restaurant tenant in a strip mall that is insured by FM Global. I have contacted the GC asking for the FM contact but thought maybe the forum could provide some insight. 1)Does FM allow reduced design areas? 2)Seating area 01./1500 +100gpm and kitchen 0.15/1500 +250gpm sound right?

Thanks,

Dewayne