To follow what Todd said,

FM 3-26 should get you started as it outlines the occupancy, description of 
occupancy, and exceptions for each Hazard Category.  HC-1 is .1/1500, HC-2 is 
.2/2500, HC-3 is .3/2500, for Wet systems with Ceilings up to 30ft.

Although both are listed as HC-1, I would be wary of doing the kitchen as HC-1 
if you are contracted to provide a NFPA 13 system AND FM approved system.  NFPA 
13 has Restaurant Service Areas listed as OH1 (.15/1500).

This is one of those cases where NFPA 13 and FM don't quite agree with each 
other.  When we have run across this, to comply with both, we design the 
systems for the worst cases .1/1500 for seating, .15/1500 for kitchen, 250 
hose, no reduction to area.  Sometimes, when faced with "box checkers", we have 
provided two separate cover sheets based on which design requirements that "box 
checker" is using.  Even though the system has been designed for worst case.

Thanks,
Sean VG





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Todd Williams
Sent: Thursday, September 29, 2016 7:24 AM
To: [email protected]
Subject: Re: FM Global

[https://tr.cloudmagic.com/h/v6/emailtag/tag/1475159036/01c6e4fe7e8b46e8dfef813adf427213/ecdd64c309bb34b23eb65c654267bfff/1e3afee3ba43649e51196c98cc753efc/9efab2399c7c560b34de477b9aa0a465/ufo.gif]
FM has different design categories (HC-1, HC-2, etc). Min hose is 250. No 
design area reductions. Their Data Sheets are on line but always best to talk 
to a rep
via Newton 
Mail<https://cloudmagic.com/k/d/mailapp?ct=pi&cv=9.1.9&pv=10.0.1&source=email_footer_2>

On Thu, Sep 29, 2016 at 7:13 AM, Dewayne Martinez 
<[email protected]<mailto:[email protected]>> wrote:
We are doing a small restaurant tenant in a strip mall that is insured by FM 
Global. I have contacted the GC asking for the FM contact but thought maybe the 
forum could provide some insight. 1)Does FM allow reduced design areas? 
2)Seating area 01./1500 +100gpm and kitchen 0.15/1500 +250gpm sound right?
Thanks,
Dewayne