Hi Dewayne.

 

Accord to 3-26 table 1. Both areas Seating areas and kitchen are a HC1 Hazard 
and sprinkler design is 0.1/1500 + 250 gpm using a 5.6 k factor sprinklers.

Also you need to wait for FM insurance recommendations.

 

CLR

 

De: Sprinklerforum [mailto:[email protected]] En 
nombre de Dewayne Martinez
Enviado el: jueves, 29 de septiembre de 2016 08:14 a. m.
Para: [email protected]
Asunto: FM Global

 

We are doing a small restaurant tenant in a strip mall that is insured by FM 
Global.  I have contacted the GC asking for the FM contact but thought maybe 
the forum could provide some insight.  1)Does FM allow reduced design areas? 
2)Seating area 01./1500 +100gpm and kitchen 0.15/1500 +250gpm sound right?

Thanks,

Dewayne 