When I have done “non-factory” projects with FM global (most recently a 
retirement home) they were very flexible in modifying their requirements to 
suit the project. In occupancies that don’t directly correlate to their core 
business I have had good luck with compromises.

Cesar is right  – confirm all design guidelines in writing from FM if they are 
any different from the ones spelled out in the data sheets.

Matt Grisé PE*, LEED AP, NICET II
Vice President – New Construction
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Cesar Lira
Sent: Thursday, September 29, 2016 9:31 AM
To: [email protected]
Subject: RE: FM Global

Hi Dewayne.

Accord to 3-26 table 1. Both areas Seating areas and kitchen are a HC1 Hazard 
and sprinkler design is 0.1/1500 + 250 gpm using a 5.6 k factor sprinklers.
Also you need to wait for FM insurance recommendations.

CLR

De: Sprinklerforum [mailto:[email protected]] En 
nombre de Dewayne Martinez
Enviado el: jueves, 29 de septiembre de 2016 08:14 a. m.
Para: 
[email protected]<mailto:[email protected]>
Asunto: FM Global

We are doing a small restaurant tenant in a strip mall that is insured by FM 
Global.  I have contacted the GC asking for the FM contact but thought maybe 
the forum could provide some insight.  1)Does FM allow reduced design areas? 
2)Seating area 01./1500 +100gpm and kitchen 0.15/1500 +250gpm sound right?
Thanks,
Dewayne