FM and xl gaps requires isolation valves and it's a good operationally practice because someone will break a head or line
Sent from my Verizon 4G LTE Droid On Oct 12, 2016 5:25 PM, "Travis Mack, SET" <[email protected]> wrote: Don't you want the racks separately controlled because they are susceptible to physical damage. If you damage a rack sprinkler, you can shut it off and keep the overhead active. In your case, if you need to shut down the racks, you also shut down the adjacent overhead system. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected]<mailto:email:[email protected]> http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack On 10/12/2016 2:18 PM, rongreenman . wrote: Why is it zoned? Just because it's bigger than 52K? One big open space? Not trying to be a smart ass (or maybe I am) but the FD won't fight a fire in zone 2 that is happening in Zone 1 bec aide an annunciation says here, not there, and it sounds like they'd be able too see the fire on entry. On Wednesday, October 12, 2016, James Crawford <[email protected]<mailto:[email protected]>> wrote: I just came from a building where the in-rack sprinklers are connected into the adjacent roof system. The building has two roof zones, north and south, the in-racks are in the north zone but connected into the south zone (no control valve at the connection point) I have never ever thought of doing this as it would send two different signals in the event of a fire, but cannot seem to find anything that says you can’t do this, with the exception of alarm signals. Any comments on this arrangement? Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email [email protected] -- Sent from Gmail Mobile _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org