Don't you want the racks separately controlled because they are
susceptible to physical damage. If you damage a rack sprinkler, you can
shut it off and keep the overhead active. In your case, if you need to
shut down the racks, you also shut down the adjacent overhead system.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 10/12/2016 2:18 PM, rongreenman . wrote:
Why is it zoned? Just because it's bigger than 52K? One big open
space? Not trying to be a smart ass (or maybe I am) but the FD won't
fight a fire in zone 2 that is happening in Zone 1 bec aide an
annunciation says here, not there, and it sounds like they'd be able
too see the fire on entry.
On Wednesday, October 12, 2016, James Crawford
<[email protected] <mailto:[email protected]>> wrote:
I just came from a building where the in-rack sprinklers are
connected into the adjacent roof system.
The building has two roof zones, north and south, the in-racks are
in the north zone but connected into the south zone (no control
valve at the connection point)
I have never ever thought of doing this as it would send two
different signals in the event of a fire, but cannot seem to find
anything that says you can’t do this, with the exception of alarm
signals.
Any comments on this arrangement?
Thank you
James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email [email protected]
<javascript:_e(%7B%7D,'cvml','[email protected]');>
--
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org