The building is 70,000 sq ft and a multi-tenant building
Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email [email protected] From: Sprinklerforum [mailto:[email protected]] On Behalf Of rongreenman . Sent: Wednesday, October 12, 2016 2:19 PM To: [email protected] Subject: Re: In-Rack Sprinkler Control Valve Why is it zoned? Just because it's bigger than 52K? One big open space? Not trying to be a smart ass (or maybe I am) but the FD won't fight a fire in zone 2 that is happening in Zone 1 bec aide an annunciation says here, not there, and it sounds like they'd be able too see the fire on entry. On Wednesday, October 12, 2016, James Crawford <[email protected]> wrote: I just came from a building where the in-rack sprinklers are connected into the adjacent roof system. The building has two roof zones, north and south, the in-racks are in the north zone but connected into the south zone (no control valve at the connection point) I have never ever thought of doing this as it would send two different signals in the event of a fire, but cannot seem to find anything that says you can’t do this, with the exception of alarm signals. Any comments on this arrangement? Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email [email protected] <javascript:_e(%7B%7D,'cvml','[email protected]');> -- Sent from Gmail Mobile